Got it now, here in WI as long as you don't touch the existing check it doesn't 
have to be updated. 

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Monday, September 27, 2010 11:45 AM
To: [email protected]
Subject: RE: tapping fire lead in for domestic

Because what is being said is that an additional backflow may be required on 
the sprinkler side of the dom. tap to prevent cross-contamination of the dom. 
System from the sprinklers.  But the question is how is the existing domestic 
supply protected from the existing sprinkler system now?

Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SCĀ  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Dewayne Martinez
Sent: Monday, September 27, 2010 12:39 PM
To: [email protected]
Subject: RE: tapping fire lead in for domestic

If the domestic was tapped into the lead in before the alarm check and the 
appropriate backflow preventer was installed in the plumbing line why would 
this affect the sprinkler calcs?  13 does not require us to add in the domestic 
demand so I am a bit confused.  
Dewayne  

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Thom
Sent: Monday, September 27, 2010 10:47 AM
To: [email protected]
Subject: RE: tapping fire lead in for domestic

Taping the fire lead if allowed by the water purveyor, will alter the calc for 
the fire since now a RPZ must be installed on the riser after that tap for 
domestic. A re-calc is the only appropriate thing to do.
That is after an internal inspection of the existing pipe to determine if the C 
is even close to 120. (Clean smooth bore) If the interior is anything but 
smooth it's just a guessing game, unless you run flow tests on each pipe 
segment. Typically we see these abandoned grocery store when they are at least 
30 yrs old, and they never have had any internal pipe inspection done.

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Friday, September 24, 2010 9:07 AM
To: [email protected]
Subject: Re: tapping fire lead in for domestic

We are remodeling an an old grocery store, being converted into a church. 
The existing fire sprinkler is pipe schedule, 3 in lead in. Wet system, alarm 
check valve with an anti freeze loop. Off of city supply. 
Existing domestic supply is well water. The owner intends to tap the fire main 
lead in to run 1" domestic. 
My concern is that he is creating a cross connection with the fire sprinkler 
water and anti freeze loop. 
My secondary concern is tapping the fire sprinkler riser....should i recommend 
hydraulic calcs since they are modifying the supply of this existing pipe 
schedule system? 

I intend to notify the owner of my concerns in writing and recommend he consult 
with his Architect and Plumbing Engineer. Any recommendations?

Forrest Wilson
Cherokee Fire 


Sent from my Verizon Wireless Phone

----- Reply message -----
From: "Ron Greenman" <[email protected]>
Date: Fri, Sep 24, 2010 10:26 am
Subject: Pool as a water source
To: <[email protected]>

You can also use the pool for a heat  sink for heat pumps and use a solar array 
to heat the pool to 50 degrees in winter (no freezing and the optimum heat 
transfer temperature for heat pump efficiency.
Engineering kids. We're part of a group building a building. We don't drive the 
project nor is our part of the project an entity in a vacuum.

On Fri, Sep 24, 2010 at 6:16 AM, Jamie.seidl <[email protected]>
wrote:
> I've done it here in Charlotte.  No problems out of it yet, but it was
just the secondary source.  We had an issue recently on a project that was a 
few years old where we had to prove the velocity at the roof top pool with a 
supply calc for the lowest system.  The health department accepted it and they 
re-opened the pool the next week. I would stress 2 inlets.  The pool contractor 
said that the largest inlet had a gpm velocity limit of 1400 gpm?  Maybe that 
was for both?
> As far as a vortex plate, when we tested the pool, a vortex didn't
develop until we had less than 1' of water left, approx 40,000 gallons already 
pumped, while my demand was around 32,000 gallons.  I still sleep well at night.
>
> Jamie
> Sent from my iPhone
>
> On Sep 24, 2010, at 8:12 AM, "Dewayne Martinez" <[email protected]>
wrote:
>
>> We have a owner that is requesting us to explore the possibility that

>> a indoor pool be used as a water source for the sprinkler system.
>> Anybody do this before?  Seems like there would be too many problems 
>> with the chlorine in the water damaging the system components.
>> Thanks,
>> Dewayne Martinez
>> Design Build Fire Protection
>> New Berlin, WI
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email
>> to:[email protected]
>> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email
> to:[email protected]
> (Put the word unsubscribe in the subject field)
>



--
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
AFSA, SFPE, ASCET, NFPA, NFSA, AFAA, ASEE, NIBS, WSAFM, WFC

They are happy men whose natures sort with their vocations. -Francis
Bacon, essayist, philosopher, and statesman (1561-1626)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to