Apparently no one liked this so I'll venture an OPINION. If one of the criteria for omitting sprinklers from a space is a non-combustible or limited combustible concealed space, and this area you've described is concealed (despite being able to see into it-transparency not being part of the definition for concealed in this context) then the question revolves around the combustibility of the plastic panels above and below. I doubt if there's a non-combustible plastic panel but there may be one that falls within the limited combustibility definition. Of course both conjectures are purely speculative.
On Mon, Sep 27, 2010 at 7:23 AM, Frans Stoop <[email protected]> wrote: > My apologies: first message had wrong subject in header. > > Dear colleagues, > > A client has a truck loading building where tankers are filled with > combustible (edible) oil. The building is protected by a foam/water > sprinkler system according to NFPA 13 & 16. > > There are a few skylights, distributed over the roof of the building. > Spacing between the skylights exceeds 10 ft (3 m). The area of each skylight > exceeds 32 ft2 (3 m²). > The skylights have plastic covers. > The bottom of each skylight is closed with a transparant plastic panel that > flattens out the bottom of the skylight with the surrounding ceiling. > The plastic cover on top and the plastic panel at the bottom create inside > the skylight a concealed space with a height of approx. 2 or 3 ft. > > The roof is covered with non-combustible ceramic insulation (rockwool) and > bitumic sheeting on top of it. > > Question: are sprinklers required in these skylights? What is your opinion? > > > Frans Stoop > TOS architecture & fire protection > Netherlands <[email protected]> > Tel. +31-24-324 0112 > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) > -- Ron Greenman Instructor Fire Protection Engineering Technology Bates Technical College 1101 So. Yakima Ave. Tacoma, WA 98405 [email protected] http://www.bates.ctc.edu/fireprotection/ 253.680.7346 253.576.9700 (cell) Member: AFSA, SFPE, ASCET, NFPA, NFSA, AFAA, ASEE, NIBS, WSAFM, WFC They are happy men whose natures sort with their vocations. -Francis Bacon, essayist, philosopher, and statesman (1561-1626) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)