Apparently no one liked this so I'll venture an OPINION. If one of the
criteria for omitting sprinklers from a space is a non-combustible or
limited combustible concealed space, and this area you've described is
concealed (despite being able to see into it-transparency not being
part of the definition for concealed in this context) then the
question revolves around the combustibility of the plastic panels
above and below. I doubt if there's a non-combustible plastic panel
but there may be one that falls within the limited combustibility
definition. Of course both conjectures are purely speculative.

On Mon, Sep 27, 2010 at 7:23 AM, Frans Stoop <[email protected]> wrote:
> My apologies: first message had wrong subject in header.
>
> Dear colleagues,
>
> A client has a truck loading building where tankers are filled with
> combustible (edible) oil. The building is protected by a foam/water
> sprinkler system according to NFPA 13 & 16.
>
> There are a few skylights, distributed over the roof of the building.
> Spacing between the skylights exceeds 10 ft (3 m). The area of each skylight
> exceeds 32 ft2 (3 m²).
> The skylights have plastic covers.
> The bottom of each skylight is closed with a transparant plastic panel that
> flattens out the bottom of the skylight with the surrounding ceiling.
> The plastic cover on top and the plastic panel at the bottom create inside
> the skylight a concealed space with a height of approx. 2 or 3 ft.
>
> The roof is covered with non-combustible ceramic insulation (rockwool) and
> bitumic sheeting on top of it.
>
> Question: are sprinklers required in these skylights? What is your opinion?
>
>
> Frans Stoop
> TOS architecture & fire protection
> Netherlands <[email protected]>
> Tel. +31-24-324 0112
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
AFSA, SFPE, ASCET, NFPA, NFSA, AFAA, ASEE, NIBS, WSAFM, WFC

They are happy men whose natures sort with their vocations. -Francis
Bacon, essayist, philosopher, and statesman (1561-1626)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to