Is it possible that one of the panels (the lower,maybe) is designed as a "drop 
out" panel?This may solve the issue.Then what is the purpose of the lower panel?


---- Ron Greenman <[email protected]> wrote: 
> Apparently no one liked this so I'll venture an OPINION. If one of the
> criteria for omitting sprinklers from a space is a non-combustible or
> limited combustible concealed space, and this area you've described is
> concealed (despite being able to see into it-transparency not being
> part of the definition for concealed in this context) then the
> question revolves around the combustibility of the plastic panels
> above and below. I doubt if there's a non-combustible plastic panel
> but there may be one that falls within the limited combustibility
> definition. Of course both conjectures are purely speculative.
> 
> On Mon, Sep 27, 2010 at 7:23 AM, Frans Stoop <[email protected]> wrote:
> > My apologies: first message had wrong subject in header.
> >
> > Dear colleagues,
> >
> > A client has a truck loading building where tankers are filled with
> > combustible (edible) oil. The building is protected by a foam/water
> > sprinkler system according to NFPA 13 & 16.
> >
> > There are a few skylights, distributed over the roof of the building.
> > Spacing between the skylights exceeds 10 ft (3 m). The area of each skylight
> > exceeds 32 ft2 (3 m²).
> > The skylights have plastic covers.
> > The bottom of each skylight is closed with a transparant plastic panel that
> > flattens out the bottom of the skylight with the surrounding ceiling.
> > The plastic cover on top and the plastic panel at the bottom create inside
> > the skylight a concealed space with a height of approx. 2 or 3 ft.
> >
> > The roof is covered with non-combustible ceramic insulation (rockwool) and
> > bitumic sheeting on top of it.
> >
> > Question: are sprinklers required in these skylights? What is your opinion?
> >
> >
> > Frans Stoop
> > TOS architecture & fire protection
> > Netherlands <[email protected]>
> > Tel. +31-24-324 0112
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > For Technical Assistance, send an email to: [email protected]
> >
> > To Unsubscribe, send an email to:[email protected]
> > (Put the word unsubscribe in the subject field)
> >
> 
> 
> 
> -- 
> Ron Greenman
> Instructor
> Fire Protection Engineering Technology
> Bates Technical College
> 1101 So. Yakima Ave.
> Tacoma, WA 98405
> 
> [email protected]
> 
> http://www.bates.ctc.edu/fireprotection/
> 
> 253.680.7346
> 253.576.9700 (cell)
> 
> Member:
> AFSA, SFPE, ASCET, NFPA, NFSA, AFAA, ASEE, NIBS, WSAFM, WFC
> 
> They are happy men whose natures sort with their vocations. -Francis
> Bacon, essayist, philosopher, and statesman (1561-1626)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> For Technical Assistance, send an email to: [email protected]
> 
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to