I'd say the letter is the first step- to the pastor or building committee
chair, someone OTHER THAN the supt refusing the work.
Note that they'll be ripping open the work to install sprinklers inside it
if relevant to the construction type and materials.
Note it is a code requirement and required for life safety as well as
property protection.
Prolly good to bring up the N word, N E G L I G E N C E if anyone is ever
hurt, since they've been advised they are ignoring the code. Possibly better
to add this verbally when telling them about the letter, either before you
send (possibly negating the reason for it if they cave) or as a follow up to
confirm it was received, understood, and then mention the downside- added
cost and/or Negligence. You'll prolly sound badge-heavy if you put
Negligence in the letter, although it depends on your perception of the
client. Noting that no A Certificate could be turned over would be
sufficient hammer- hopefully.

Your call to the AHJ- fine line to walk. If you know em, have a rapport with
em, make the call. If you don't know em from Adam, he may be best friends
with the supt and you've shot yourself in the foot. 
We got a call from a strip center owner who we've worked for off and on over
the years. Seems the pump and tank were abandoned 10 years ago just before
he bought the place, and a new waterline was run into the back of the
building. However, no BFPs were installed, WFS were built but not wired, and
the service was never switched over. Yes, 100,000 SF of dumpy strip center
was left unprotected for a decade. Yes, in the state that was first with the
IRC mandate, evidently no one in Harrisburg has seen NFPA 25. Anyway, it
came to light when a competitor went in to move heads for a new tenant, and
the system was off. In addition to calling the Owner, he called the BCO
(AHJ) who gave the Owner 48 hrs to cease operating the center. A little
tough with a dozen stores in operation! We were given the job, he certainly
wasn't going to call the guy that turned him in hoping since he was there
and the AHJ gave em a short time period to start repairs, he'd get the job.
Doesn't get that cold up here.

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Eric Tysinger
Sent: Tuesday, October 05, 2010 10:22 AM
To: [email protected]
Subject: RE: Owner refusal

A quick little heads up call to the AHJ/Inspector before the inspection does
wonders for situations like that. 


Thanks,
Eric Tysinger CET
NICET III - 108988
Designer
Wayne Automatic Fire Sprinklers, Inc.
4370 Motorsport Drive
Concord, NC 28027
p: (704)782-3032 x1751
f: (704)795-6838
C: (239)633-9703

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Todd - FPDC
Sent: Tuesday, October 05, 2010 10:01 AM
To: [email protected]
Subject: Owner refusal

I  just coming from a church project where they added an 8 x 16 wooden
canopy at the main entry. The project super (and also church member) has
adamantly refused to install sprinklers even though they are required. I
have told him that they are needed by Code, buy he remains defiant. I assume
that the AHJ would pick up on it during final inspection, but can't count on
it. 

My plan is to write a letter to the church (my client) stating that
protection is required by Code and is my best advice, but if they choose not
to, I am not responsible for the consequences. 

How have others handled similar situations? The inspection for CO is
schedules for Friday. 

Sent from my iPhone
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to