I came across this letter regarding the antifreeze situation.

"The XXXXXX Residence incorporated an automatic sprinkler system in response
to a variance approved by the XXXXXX zoning authority.  This automatic
sprinkler system was designed in accordance with NFPA 13D, Standard for the
Installation of Sprinkler Systems in One- and Two-Family Dwellings and
Manufactured Homes.  The scope of the system included sprinklers in
residential areas as well as in certain utility areas.  A storage tank with
a pumping system provided the water supply and pressure.  Because of a
concern for freezing conditions in the attic space, a 50% propylene glycol
antifreeze solution was added to the piping (copper).  In addition, attic
sprinkler piping was to be covered with insulating material and also routed
remotely from the eaves.

After a fire incident (resulting in a fatality and a serious injury to
another person) involving a sprinkler system with an antifreeze solution,
NFPA initiated a fire research project to assess the hazard of such systems.
The NFPA Safety Alert is enclosed for your information.  Please note that
although new residential antifreeze systems are not to be designed or
installed until final regulations are issued, guidelines for existing
systems should be followed as described.

In view of the NFPA action it is necessary to advise the client that the
automatic sprinkler system should be assessed and the antifreeze solution
changed to a maximum 40% propylene glycol concentration.  This concentration
would satisfy the NFPA guidelines and also provide protection from freezing
down to a temperature of -30 F.  This should be adequate for all but the
most extreme conditions when the home might be left without power and heat
for an extended period.

XXXXXXX (sprinkler company name) has been notified that this information
would be provided to you.  Although a maintenance contract should be in
place for this system, the NFPA Safety Alert would also be brought to the
Owner's attention by their maintenance contractor.

Let me know if I can be of any assistance to you in resolving this potential
safety issue."

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to