Dewayne,

The storage room is essentially part of the space above the ceiling so
if it's also concealed and non-combustible [ }:-)  ] then no. If not
then yes. If you separate with full height walls you need rock on the
ceiling side if you use wood studs to maintain non-combustibilty, but
not if you use steel studs. You need rock on the inside in any case.
If you have non-full height walls with wood studs even they need to be
rocked above the ceiling to maintain non/limited combustibility.
Ceiling is cheapest. The definition is to be found in the definitions
of non & limited combustible spaces where sprinklers are allowed to be
omitted. Is the space unusable? Does the construction meet the
requirement? Is the space not normally accessible from other, useable
spaces? So wherever that list of thirteen (or is it sixteen?)
conditions that allow you to omit sprinklers in the edition of 13 you
are using is, is where your argument rests.

On Fri, Oct 8, 2010 at 8:00 AM, Dewayne Martinez <[email protected]> wrote:
> Office with ceilings containing a storage room with no ceiling.  I told
> the architect that the walls for this room would have to go full height
> or else we would need to add sprinklers in the non-combustible space
> above the office.  He is looking for a specific code reference....is
> there?  For the full height wall, would it require gyp bd on one side
> only or both sides with all the gaps filled?
> Thanks,
>
> Dewayne
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
AFSA, SFPE, ASCET, NFPA, NFSA, AFAA, ASEE, NIBS, WSAFM, WFC

They are happy men whose natures sort with their vocations. -Francis
Bacon, essayist, philosopher, and statesman (1561-1626)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to