Thanks Ron, That is what I figured but thought I remember seeing a detail showing a office / warehouse example showing that the wall to be full height or sprinklers in the space above the office. Dewayne
-----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Ron Greenman Sent: Friday, October 08, 2010 10:33 AM To: [email protected] Subject: Re: Full height walls in exposed room Dewayne, The storage room is essentially part of the space above the ceiling so if it's also concealed and non-combustible [ }:-) ] then no. If not then yes. If you separate with full height walls you need rock on the ceiling side if you use wood studs to maintain non-combustibilty, but not if you use steel studs. You need rock on the inside in any case. If you have non-full height walls with wood studs even they need to be rocked above the ceiling to maintain non/limited combustibility. Ceiling is cheapest. The definition is to be found in the definitions of non & limited combustible spaces where sprinklers are allowed to be omitted. Is the space unusable? Does the construction meet the requirement? Is the space not normally accessible from other, useable spaces? So wherever that list of thirteen (or is it sixteen?) conditions that allow you to omit sprinklers in the edition of 13 you are using is, is where your argument rests. On Fri, Oct 8, 2010 at 8:00 AM, Dewayne Martinez <[email protected]> wrote: > Office with ceilings containing a storage room with no ceiling. I > told the architect that the walls for this room would have to go full > height or else we would need to add sprinklers in the non-combustible > space above the office. He is looking for a specific code > reference....is there? For the full height wall, would it require gyp > bd on one side only or both sides with all the gaps filled? > Thanks, > > Dewayne > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email > to:[email protected] > (Put the word unsubscribe in the subject field) > -- Ron Greenman Instructor Fire Protection Engineering Technology Bates Technical College 1101 So. Yakima Ave. Tacoma, WA 98405 [email protected] http://www.bates.ctc.edu/fireprotection/ 253.680.7346 253.576.9700 (cell) Member: AFSA, SFPE, ASCET, NFPA, NFSA, AFAA, ASEE, NIBS, WSAFM, WFC They are happy men whose natures sort with their vocations. -Francis Bacon, essayist, philosopher, and statesman (1561-1626) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)