If it has insulation draped from top to top of the Z purlins, you can measure from the underside of the NOMINAL DEPTH OF INSULATION and ignore where it goes back up to the top of the Z. Likely there's 8" or 10' insulation and treated like a smooth ceiling from which to measure from below its NOMINAL location.
glc -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Mike Hairfield Sent: Monday, October 25, 2010 2:44 PM To: AFSA SprinklerFORUM Subject: Maximum Deflector Distance below Z Purlins OK Metal building with 9 1/2" Z-Purlins, what is maximum distance that the deflector can be below the bottom of the Purlin. Mike _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)