If it has insulation draped from top to top of the Z purlins, you can
measure from the underside of the NOMINAL DEPTH OF INSULATION and ignore
where it goes back up to the top of the Z. Likely there's 8" or 10'
insulation and treated like a smooth ceiling from which to measure from
below its NOMINAL location.

glc

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Mike
Hairfield
Sent: Monday, October 25, 2010 2:44 PM
To: AFSA SprinklerFORUM
Subject: Maximum Deflector Distance below Z Purlins


OK Metal building with 9 1/2" Z-Purlins, what is maximum distance that the
deflector can be below the bottom of the Purlin.
 
Mike                                      