Update. I responded to Mr. Caputo by asking if it the intent to disregard 2002, 13:8.6.2.12 when determining the "Protection Area of Coverage." He replied "Negative. The sections you refer to provide spacing rules – providing the area of coverage for the sprinklers. The comment related to 11.2.3.5.2 (2) applies to the discharge flow rate which is usually taken as A x D = Q but in the case of small rooms, is technically s x l = A
I doubt anyone would complain or object if you applied the actual area of the room method to apply the density hydraulically. It’s a subtle nuance which is not addressed. I am fairly certain if a proposal were to be submitted to clarify this point, the discharge committee would agree that either method is acceptable. " So, another check in the winner's column and my faith has been restored! Carrol Glimstad ________________________________ From: Carrol Glimstad <[email protected]> To: [email protected] Sent: Tue, November 2, 2010 2:05:12 PM Subject: Re: Residential "Room Design Method"? I did go that route... I instead received a response from Mr. Caputo with NFPA and he informed me that per 2002, "...the small rooms rule is not applicable to the design consideration for residential occupancies." Unless I am wrong, (which I frequently am) although he (Roland) is a committee member of the TCC for NFPA, he is with AFSA. Trust me, I would LOVE to get an "official" response from Mr. Huggins! How would I go about getting one from AFSA (i.e. Roland) ? But I do think I will forward some excerpts of this thread and see where that gets me. (probably nowhere that I want to be...) Carrol Glimstad Sierra Fire Design 916.475.4928 ________________________________ From: "Johnson, Duane (NIH/OD/ORS) [C]" <[email protected]> To: "[email protected]" <[email protected]> Sent: Tue, November 2, 2010 12:59:44 PM Subject: RE: Residential "Room Design Method"? NFPA has an email accounts setup for all NFPA codes where you can submit questions and receive code interpretations and technical answers. The format is setup as [email protected]. Replace the # with the code you are inquiring about. For example, if you have a question related to the sprinkler code, you would submit your question to [email protected]. Then Roland can 'officially' respond. Duane Johnson, PE Program Manager Division of the Fire Marshal (Support Contractor) Office of Research Services National Institutes of Health 301-496-0487 _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)