Neither of these studies are referring to residential CPVC potable
piping but to:

 IMPACT:
Cross-connection control for Class 1 and Class 2 wet-pipe fire
sprinkler systems using approved backflow prevention assemblies on new
construction is recommended based on the following findings: (1) water
quality within the black-steel wet-pipe fire sprinkler systems exceed
drinking water standards;

The peg the hat is hung on with residential CPVC and PEX is the lead
in the heads and the stagnant water in the tree.

On Wed, Nov 3, 2010 at 2:36 PM, Forest Wilson <[email protected]> wrote:
> Please refer to the following:
>
> http://www.waterresearchfoundation.org/research/topicsandprojects/execSum/158.aspx
>
> and
>
> http://books.google.com/books?id=X-f_x07RIgQC&pg=PR26&lpg=PR26&dq=wet+sprinkler+systems+and+water+contamination&source=bl&ots=S_8_-SeIho&sig=lTvbesgZN9ZbVT5nqrH3kGmc5kM&hl=en&ei=BM_RTPW8MZWSjAeCioW4DA&sa=X&oi=book_result&ct=result&resnum=2&sqi=2&ved=0CBYQ6AEwAQ#v=onepage&q=wet%20sprinkler%20systems%20and%20water%20contamination&f=false
>
> These are reports on the impact of wet sprinkler systems on water quality.
> Testing indicates that water from fire sprinkler systems is not potable.
>
>
>
>
>
> On 11/3/2010 5:01 PM, Gary Stites wrote:
>>
>> I am actually looking for your opinions as our water purveyors are asking
>> us
>> for assistance and education...
>>
>> On Wed, Nov 3, 2010 at 1:51 PM, Gary Stites<[email protected]>  wrote:
>>
>>> The water companies in our area are concerned about backflow prevention
>>> on
>>> 13D systems. With California adopting the IRC all the AHJ's are
>>> scrambling
>>> to put their spin on it!
>>>
>>> Anyway, what are the backflow concerns on a CPVC system that is not
>>> intertwined with the plumbing system? There is talk of requiring RP
>>> devices
>>> etc. Is a check-valve not sufficient?
>>>
>>> Thank You
>>> --
>>> Gary Stites
>>> 661-213-9379
>>>
>>> www.bakersfieldnbc.org/worshipteaminfo
>>> www.wgt.com/clubs/the_lookouts/default.aspx
>>> www.sprinklersoft.net
>>> Pandora Station  http://www.pandora.com/?sc=sh43464983213902734
>>>
>>>
>>
>
>
> --
> Forest Wilson
> Project Manager
> Cherokee Fire Protection Co.
> 1855 Bellbrook Ave Ste C
> Xenia OH 45385
>
> ph: 937-376-2333
> fx: 614-455-4324
> www.cherokee-fire.com
> Visit our blog: www.cherokee-fire.blogspot.com
> *******************************************
> This email and any files transmitted with it are confidential and intended
> solely for the use of the individual or entity to whom they are addressed.
> If you have received this email in error please notify the system manager.
> This message contains confidential information and is intended only for the
> individual named. If you are not the named addressee you should not
> disseminate, distribute or copy this e-mail. Please notify the sender
> immediately by e-mail if you have received this e-mail by mistake and delete
> this e-mail from your system. If you are not the intended recipient you are
> notified that disclosing, copying, distributing or taking any action in
> reliance on the contents of this information is strictly prohibited.
> *******************************************
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
AFSA, SFPE, ASCET, NFPA, NFSA, AFAA, ASEE, NIBS, WSAFM, WFC

They are happy men whose natures sort with their vocations. -Francis
Bacon, essayist, philosopher, and statesman (1561-1626)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to