Chris,

Maybe the best place to look is in the Northridge report. 250
failures. Most if not all were attachment failures. I don't remember
if any fires were involved. Maybe one of the Californians remembers.
If I remember tomorrow I have the report at work and I'll take a look.
If you want you can send an email to remind me.

On Wed, Nov 3, 2010 at 9:51 AM, Chris Cahill <[email protected]> wrote:
> Curious question, has there ever been a loss because of the use of an older
> standard assuming it complied with any ed.?  So even with EQ were there
> systems that had fires after earthquakes where the hangers failed and there
> was a significant loss?  Or were the failures just hanger issues but no
> fires?  And even then in EQ country is there anything requiring retrofit if
> say it was built in '96?  If there was some history of failure would we
> expect the newer standards to address in Ch. 1 retroactivity?
>
> There are plenty of losses due to closed/inadequate water.  Don't see that a
> year issue.  There are a few noted as system not designed for the hazard.
> But many of these the original system was complaint but the hazard changed
> to the system never upgraded.  Or it was never right for the original
> hazard. Again I don't see this as a year issue.
>
> Chris Cahill
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of David
> Blackwell
> Sent: Wednesday, November 03, 2010 10:58 AM
> To: [email protected]
> Subject: RE: Physical Science :)
>
> Has anyone on the list gotten feedback from their insurance carrier
> regarding using an old code [like the 1996 edition mentioned in the email
> below]?
>
> I'm guessing they wouldn't like you designing to such an old code minimum
> which had inadequate minimum standards that were later fixed in newer
> editions of the code.  One glaring difference between 2010 & 1996 is in the
> area of seismic protection which was upgraded after a couple of quakes in CA
> demonstrated the code minimum requirements in that arena were insufficient.
> If I were out in private practice I would be trying to design to the current
> latest published editions so I didn't end up in court with a lawyer asking
> me why I didn't use a more current edition...
>
>
>
> David W. S. Blackwell, II, PE, CFI-I, CFPE
> Engineering
> ----------------------------------------------------------------
> Office of State Fire Marshal
> 141 Monticello Trail
> Columbia, SC 29203
> Phone:  803.896.9833
> Fax:  803.896.9806
> Email:  [email protected]
> OSFM Website: http://www.llr.state.sc.us/firemarshal.asp
> ----------------------------------------------------------------
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of
> [email protected]
> Sent: Wednesday, November 03, 2010 9:56 AM
> To: [email protected]
> Subject: RE: Physical Science :)
>
> Sorry but when doing in-depth code analysis', there is no way you could find
> every bit of information needed in a tabbed book versus doing a digital
> search unless you have all the time in the world.  There is stuff buried in
> these texts that is not in the index and unless you've stumbled across it
> before and tagged it, you'd never find it.
>
> Digital is here, now, not waiting for the next generation.
>
> As far as the question concerning why NICET uses particular versions, it is
> probably due to the amount of work involved with reworking a test.  Plus not
> all jurisdictions jump on the new Standard immediately upon its publication.
> I still have many jurisdictions using the 2002 NFPA 13 and had one earlier
> in the year that was still on the 1996 version.  It would be a significant
> task to develop a new test each time a new standard came out.
>
> Craig L. Prahl, CET
> Fire Protection
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> Spartanburg, SC  29304-0491
> Direct - 864.599.4102
> Fax - 864.599.8439
> CH2MHILL Extension  74102
> [email protected]
>
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Todd Williams
> Sent: Wednesday, November 03, 2010 9:50 AM
> To: [email protected]
> Subject: RE: Physical Science :)
>
> We old timers are used to paper, but the next generation will
> probably be much more geared to digital. Somehow NICET and others
> will need to adapt. Agencies are not going to continue print issues
> just for some open book testing agency. I agree that finding
> information in a tabbed text is still a lot quicker than a computer
> search. But perhaps testing agencies will have to provide computer
> access to certain reference materials as a part of the computer
> testing procedure.
>
> Brian, as far as your question, I have wondered that as well. Perhaps
> they use a random number generator
>
>
> At 09:21 AM 11/3/2010, you wrote:
>>Here's a question for some of you veterans, how does NICET come up with
> what
>>year code will be on the test? I don't get why some of these codes are 2,3,
>>and greater revisions behind the current one....
>>
>>Brian Harris
>>FDFP Inc.
>>
>>
>>-----Original Message-----
>>From: [email protected]
>>[mailto:[email protected]] On Behalf Of George
> Church
>>Sent: Wednesday, November 03, 2010 9:22 AM
>>To: [email protected]
>>Subject: RE: Physical Science :)
>>
>>Its not as easy as it sounds to change a 30-year old certification program
>>as you might think.
>>While it's a PIA to drag around all the reference materials, you must also
>>appreciate the numerous concerns and integrity requirements and
> restrictions
>>faced by any testing agency. They need to prevent theft of test questions,
>>they need to make sure you are using a hand calculator rather than allowing
>>the possibility you'll run a calc program on a PC or programmable
>>calculator, that you know where to look things up based on familiarity with
>>the references rather than rely on a word search, etc.
>>
>>NICET is moving along with PC-based testing at readily accessible testing
>>centers nationwide, with open scheduling and instant results. It's a large
>>undertaking with substantial volunteer contribution to make it work. To
>>speed it along, participate and donate your time and energy to the industry
>>that puts food on your table.
>>
>>NICET is also facing some competition in the market which may or may not
>>produce other streamlining of the process, but it is what it is and the
>>integrity of the process demands checking and validating the changes, and
>>that all takes time. Think of the 4 years +/- some of us have been involved
>>in the process, lugging ourselves to Alexandria, and -not to sound like the
>>proverbial schoolteacher, but I remember borrowing references from the
>>Atlanta fire marshal so I had to spend Fri afternoon going downtown,
> lugging
>>the books to the car, getting familiar with them Fri night, and lugging
> them
>>to the exam and on Monday AM back to City Hall. It builds character and
>>memories, like then-mayor Andrew Young getting in the elevator with me Fri
>>and observing what a fun weekend I must be stocking up for :)
>>
>>glc
>>
>>-----Original Message-----
>>From: [email protected]
>>[mailto:[email protected]] On Behalf Of
>>[email protected]
>>Sent: Wednesday, November 03, 2010 8:56 AM
>>To: [email protected]
>>Subject: RE: Physical Science :)
>>
>>Really, all of our codes are now in digital format.  Much easier to search
>>and cheaper for the company.  NICET needs to come into the 21st century
> with
>>this.  It's just crazy lugging 30-40 lbs of reference books to a test.  Had
>>one test that was on 2nd floor and had to tote the load up the stairs.
> Just
>>plain ridiculous.
>>
>>Craig L. Prahl, CET
>>Fire Protection
>>CH2MHILL
>>Lockwood Greene
>>1500 International Drive
>>Spartanburg, SC  29304-0491
>>Direct - 864.599.4102
>>Fax - 864.599.8439
>>CH2MHILL Extension  74102
>>[email protected]
>>
>>
>>-----Original Message-----
>>From: [email protected]
>>[mailto:[email protected]] On Behalf Of Todd
> Williams
>>Sent: Tuesday, November 02, 2010 7:08 PM
>>To: [email protected]
>>Subject: Re: Physical Science :)
>>
>>And don't forget to put index tabs on your references and take a
>>dictionary with you.
>>
>>What are they going to do when al this stuff is on our iPads?
>>
>>
>>At 06:39 PM 11/2/2010, you wrote:
>> >Same here, Brian.  Of course I'm so old that when I took it with me
>> >it was only one volume, not two.
>> >--
>> >
>> >PARSLEY CONSULTING
>> >
>> >Ken Wagoner, SET
>> >
>> >760.745.6181 voice
>> >
>> >760.745.0537 fax
>> >
>> >[email protected] <mailto:[email protected]>e-mail
>> >
>> >www.ParsleyConsulting.com <http://www.ParsleyConsulting.com>website
>> >
>> >
>> >
>> >
>> >On 11/2/2010 2:46 PM, Jamie.seidl wrote:
>> >>The fire protection handbook. It's all I used.
>> >>
>> >>Jamie
>> >>Sent from my iPhone
>> >>
>> >>On Nov 2, 2010, at 5:08 PM, "Brian
>> >>Harris"<[email protected]>  wrote:
>> >>
>> >>>Any recommendations for good reference material for the Physical
> Science
>> >>>portion of the Nicet test?
>> >>>
>> >>>
>> >>>
>> >>>Brian Harris
>> >>>
>> >>>First Defense Fire Protection
>> >>>
>> >>>11957 Ramah Church Road
>> >>>
>> >>>Huntersville, NC 28078
>> >>>
>> >>>Phone: 704.948.3506
>> >>>
>> >>>Fax: 704.948.3507
>> >>>
>> >>>Nicet # 128476
>> >>>
>> >>>
>> >>>
>> >>>
>> >>>
>> >>>
>> >>>
>> >>>=======
>> >>>Email scanned by PC Tools - No viruses or spyware found.
>> >>>(Email Guard: 7.0.0.21, Virus/Spyware Database: 6.16210)
>> >>>http://www.pctools.com/
>> >>>=======
>> >>>_______________________________________________
>> >>>Sprinklerforum mailing list
>> >>>[email protected]
>> >>>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>> >>>
>> >>>For Technical Assistance, send an email to: [email protected]
>> >>>
>> >>>To Unsubscribe, send an email
> to:[email protected]
>> >>>(Put the word unsubscribe in the subject field)
>> >>_______________________________________________
>> >>Sprinklerforum mailing list
>> >>[email protected]
>> >>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>> >>
>> >>For Technical Assistance, send an email to: [email protected]
>> >>
>> >>To Unsubscribe, send an email
> to:[email protected]
>> >>(Put the word unsubscribe in the subject field)
>> >_______________________________________________
>> >Sprinklerforum mailing list
>> >[email protected]
>> >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>> >
>> >For Technical Assistance, send an email to: [email protected]
>> >
>> >To Unsubscribe, send an email to:[email protected]
>> >(Put the word unsubscribe in the subject field)
>>
>>Todd G. Williams, PE
>>Fire Protection Design/Consulting
>>Stonington, CT
>>860.535.2080
>>www.fpdc.com
>>
>>_______________________________________________
>>Sprinklerforum mailing list
>>[email protected]
>>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>>For Technical Assistance, send an email to: [email protected]
>>
>>To Unsubscribe, send an email to:[email protected]
>>(Put the word unsubscribe in the subject field)
>>_______________________________________________
>>Sprinklerforum mailing list
>>[email protected]
>>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>>For Technical Assistance, send an email to: [email protected]
>>
>>To Unsubscribe, send an email to:[email protected]
>>(Put the word unsubscribe in the subject field)
>>
>>_______________________________________________
>>Sprinklerforum mailing list
>>[email protected]
>>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>>For Technical Assistance, send an email to: [email protected]
>>
>>To Unsubscribe, send an email to:[email protected]
>>(Put the word unsubscribe in the subject field)
>>
>>
>>
>>
>>
>>=======
>>Email scanned by PC Tools - No viruses or spyware found.
>>(Email Guard: 7.0.0.21, Virus/Spyware Database: 6.16220)
>>http://www.pctools.com/
>>=======
>>
>>
>>
>>
>>
>>=======
>>Email scanned by PC Tools - No viruses or spyware found.
>>(Email Guard: 7.0.0.21, Virus/Spyware Database: 6.16220)
>>http://www.pctools.com/
>>=======
>>_______________________________________________
>>Sprinklerforum mailing list
>>[email protected]
>>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>>For Technical Assistance, send an email to: [email protected]
>>
>>To Unsubscribe, send an email to:[email protected]
>>(Put the word unsubscribe in the subject field)
>
> Todd G. Williams, PE
> Fire Protection Design/Consulting
> Stonington, CT
> 860.535.2080
> www.fpdc.com
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
AFSA, SFPE, ASCET, NFPA, NFSA, AFAA, ASEE, NIBS, WSAFM, WFC

They are happy men whose natures sort with their vocations. -Francis
Bacon, essayist, philosopher, and statesman (1561-1626)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to