I looked at the Northridge report this morning and it has nothing on
fires, just attachment, hanger and bracing failures.

On Wed, Nov 3, 2010 at 7:10 PM, Ron Greenman <[email protected]> wrote:
> Chris,
>
> Maybe the best place to look is in the Northridge report. 250
> failures. Most if not all were attachment failures. I don't remember
> if any fires were involved. Maybe one of the Californians remembers.
> If I remember tomorrow I have the report at work and I'll take a look.
> If you want you can send an email to remind me.
>
> On Wed, Nov 3, 2010 at 9:51 AM, Chris Cahill <[email protected]> wrote:
>> Curious question, has there ever been a loss because of the use of an older
>> standard assuming it complied with any ed.?  So even with EQ were there
>> systems that had fires after earthquakes where the hangers failed and there
>> was a significant loss?  Or were the failures just hanger issues but no
>> fires?  And even then in EQ country is there anything requiring retrofit if
>> say it was built in '96?  If there was some history of failure would we
>> expect the newer standards to address in Ch. 1 retroactivity?
>>
>> There are plenty of losses due to closed/inadequate water.  Don't see that a
>> year issue.  There are a few noted as system not designed for the hazard.
>> But many of these the original system was complaint but the hazard changed
>> to the system never upgraded.  Or it was never right for the original
>> hazard. Again I don't see this as a year issue.
>>
>> Chris Cahill
>>
>> -----Original Message-----
>> From: [email protected]
>> [mailto:[email protected]] On Behalf Of David
>> Blackwell
>> Sent: Wednesday, November 03, 2010 10:58 AM
>> To: [email protected]
>> Subject: RE: Physical Science :)
>>
>> Has anyone on the list gotten feedback from their insurance carrier
>> regarding using an old code [like the 1996 edition mentioned in the email
>> below]?
>>
>> I'm guessing they wouldn't like you designing to such an old code minimum
>> which had inadequate minimum standards that were later fixed in newer
>> editions of the code.  One glaring difference between 2010 & 1996 is in the
>> area of seismic protection which was upgraded after a couple of quakes in CA
>> demonstrated the code minimum requirements in that arena were insufficient.
>> If I were out in private practice I would be trying to design to the current
>> latest published editions so I didn't end up in court with a lawyer asking
>> me why I didn't use a more current edition...
>>
>>
>>
>> David W. S. Blackwell, II, PE, CFI-I, CFPE
>> Engineering
>> ----------------------------------------------------------------
>> Office of State Fire Marshal
>> 141 Monticello Trail
>> Columbia, SC 29203
>> Phone:  803.896.9833
>> Fax:  803.896.9806
>> Email:  [email protected]
>> OSFM Website: http://www.llr.state.sc.us/firemarshal.asp
>> ----------------------------------------------------------------
>>
>> -----Original Message-----
>> From: [email protected]
>> [mailto:[email protected]] On Behalf Of
>> [email protected]
>> Sent: Wednesday, November 03, 2010 9:56 AM
>> To: [email protected]
>> Subject: RE: Physical Science :)
>>
>> Sorry but when doing in-depth code analysis', there is no way you could find
>> every bit of information needed in a tabbed book versus doing a digital
>> search unless you have all the time in the world.  There is stuff buried in
>> these texts that is not in the index and unless you've stumbled across it
>> before and tagged it, you'd never find it.
>>
>> Digital is here, now, not waiting for the next generation.
>>
>> As far as the question concerning why NICET uses particular versions, it is
>> probably due to the amount of work involved with reworking a test.  Plus not
>> all jurisdictions jump on the new Standard immediately upon its publication.
>> I still have many jurisdictions using the 2002 NFPA 13 and had one earlier
>> in the year that was still on the 1996 version.  It would be a significant
>> task to develop a new test each time a new standard came out.
>>
>> Craig L. Prahl, CET
>> Fire Protection
>> CH2MHILL
>> Lockwood Greene
>> 1500 International Drive
>> Spartanburg, SC  29304-0491
>> Direct - 864.599.4102
>> Fax - 864.599.8439
>> CH2MHILL Extension  74102
>> [email protected]
>>
>>
>>
>> -----Original Message-----
>> From: [email protected]
>> [mailto:[email protected]] On Behalf Of Todd Williams
>> Sent: Wednesday, November 03, 2010 9:50 AM
>> To: [email protected]
>> Subject: RE: Physical Science :)
>>
>> We old timers are used to paper, but the next generation will
>> probably be much more geared to digital. Somehow NICET and others
>> will need to adapt. Agencies are not going to continue print issues
>> just for some open book testing agency. I agree that finding
>> information in a tabbed text is still a lot quicker than a computer
>> search. But perhaps testing agencies will have to provide computer
>> access to certain reference materials as a part of the computer
>> testing procedure.
>>
>> Brian, as far as your question, I have wondered that as well. Perhaps
>> they use a random number generator
>>
>>
>> At 09:21 AM 11/3/2010, you wrote:
>>>Here's a question for some of you veterans, how does NICET come up with
>> what
>>>year code will be on the test? I don't get why some of these codes are 2,3,
>>>and greater revisions behind the current one....
>>>
>>>Brian Harris
>>>FDFP Inc.
>>>
>>>
>>>-----Original Message-----
>>>From: [email protected]
>>>[mailto:[email protected]] On Behalf Of George
>> Church
>>>Sent: Wednesday, November 03, 2010 9:22 AM
>>>To: [email protected]
>>>Subject: RE: Physical Science :)
>>>
>>>Its not as easy as it sounds to change a 30-year old certification program
>>>as you might think.
>>>While it's a PIA to drag around all the reference materials, you must also
>>>appreciate the numerous concerns and integrity requirements and
>> restrictions
>>>faced by any testing agency. They need to prevent theft of test questions,
>>>they need to make sure you are using a hand calculator rather than allowing
>>>the possibility you'll run a calc program on a PC or programmable
>>>calculator, that you know where to look things up based on familiarity with
>>>the references rather than rely on a word search, etc.
>>>
>>>NICET is moving along with PC-based testing at readily accessible testing
>>>centers nationwide, with open scheduling and instant results. It's a large
>>>undertaking with substantial volunteer contribution to make it work. To
>>>speed it along, participate and donate your time and energy to the industry
>>>that puts food on your table.
>>>
>>>NICET is also facing some competition in the market which may or may not
>>>produce other streamlining of the process, but it is what it is and the
>>>integrity of the process demands checking and validating the changes, and
>>>that all takes time. Think of the 4 years +/- some of us have been involved
>>>in the process, lugging ourselves to Alexandria, and -not to sound like the
>>>proverbial schoolteacher, but I remember borrowing references from the
>>>Atlanta fire marshal so I had to spend Fri afternoon going downtown,
>> lugging
>>>the books to the car, getting familiar with them Fri night, and lugging
>> them
>>>to the exam and on Monday AM back to City Hall. It builds character and
>>>memories, like then-mayor Andrew Young getting in the elevator with me Fri
>>>and observing what a fun weekend I must be stocking up for :)
>>>
>>>glc
>>>
>>>-----Original Message-----
>>>From: [email protected]
>>>[mailto:[email protected]] On Behalf Of
>>>[email protected]
>>>Sent: Wednesday, November 03, 2010 8:56 AM
>>>To: [email protected]
>>>Subject: RE: Physical Science :)
>>>
>>>Really, all of our codes are now in digital format.  Much easier to search
>>>and cheaper for the company.  NICET needs to come into the 21st century
>> with
>>>this.  It's just crazy lugging 30-40 lbs of reference books to a test.  Had
>>>one test that was on 2nd floor and had to tote the load up the stairs.
>> Just
>>>plain ridiculous.
>>>
>>>Craig L. Prahl, CET
>>>Fire Protection
>>>CH2MHILL
>>>Lockwood Greene
>>>1500 International Drive
>>>Spartanburg, SC  29304-0491
>>>Direct - 864.599.4102
>>>Fax - 864.599.8439
>>>CH2MHILL Extension  74102
>>>[email protected]
>>>
>>>
>>>-----Original Message-----
>>>From: [email protected]
>>>[mailto:[email protected]] On Behalf Of Todd
>> Williams
>>>Sent: Tuesday, November 02, 2010 7:08 PM
>>>To: [email protected]
>>>Subject: Re: Physical Science :)
>>>
>>>And don't forget to put index tabs on your references and take a
>>>dictionary with you.
>>>
>>>What are they going to do when al this stuff is on our iPads?
>>>
>>>
>>>At 06:39 PM 11/2/2010, you wrote:
>>> >Same here, Brian.  Of course I'm so old that when I took it with me
>>> >it was only one volume, not two.
>>> >--
>>> >
>>> >PARSLEY CONSULTING
>>> >
>>> >Ken Wagoner, SET
>>> >
>>> >760.745.6181 voice
>>> >
>>> >760.745.0537 fax
>>> >
>>> >[email protected] <mailto:[email protected]>e-mail
>>> >
>>> >www.ParsleyConsulting.com <http://www.ParsleyConsulting.com>website
>>> >
>>> >
>>> >
>>> >
>>> >On 11/2/2010 2:46 PM, Jamie.seidl wrote:
>>> >>The fire protection handbook. It's all I used.
>>> >>
>>> >>Jamie
>>> >>Sent from my iPhone
>>> >>
>>> >>On Nov 2, 2010, at 5:08 PM, "Brian
>>> >>Harris"<[email protected]>  wrote:
>>> >>
>>> >>>Any recommendations for good reference material for the Physical
>> Science
>>> >>>portion of the Nicet test?
>>> >>>
>>> >>>
>>> >>>
>>> >>>Brian Harris
>>> >>>
>>> >>>First Defense Fire Protection
>>> >>>
>>> >>>11957 Ramah Church Road
>>> >>>
>>> >>>Huntersville, NC 28078
>>> >>>
>>> >>>Phone: 704.948.3506
>>> >>>
>>> >>>Fax: 704.948.3507
>>> >>>
>>> >>>Nicet # 128476
>>> >>>
>>> >>>
>>> >>>
>>> >>>
>>> >>>
>>> >>>
>>> >>>
>>> >>>=======
>>> >>>Email scanned by PC Tools - No viruses or spyware found.
>>> >>>(Email Guard: 7.0.0.21, Virus/Spyware Database: 6.16210)
>>> >>>http://www.pctools.com/
>>> >>>=======
>>> >>>_______________________________________________
>>> >>>Sprinklerforum mailing list
>>> >>>[email protected]
>>> >>>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>> >>>
>>> >>>For Technical Assistance, send an email to: [email protected]
>>> >>>
>>> >>>To Unsubscribe, send an email
>> to:[email protected]
>>> >>>(Put the word unsubscribe in the subject field)
>>> >>_______________________________________________
>>> >>Sprinklerforum mailing list
>>> >>[email protected]
>>> >>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>> >>
>>> >>For Technical Assistance, send an email to: [email protected]
>>> >>
>>> >>To Unsubscribe, send an email
>> to:[email protected]
>>> >>(Put the word unsubscribe in the subject field)
>>> >_______________________________________________
>>> >Sprinklerforum mailing list
>>> >[email protected]
>>> >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>> >
>>> >For Technical Assistance, send an email to: [email protected]
>>> >
>>> >To Unsubscribe, send an email to:[email protected]
>>> >(Put the word unsubscribe in the subject field)
>>>
>>>Todd G. Williams, PE
>>>Fire Protection Design/Consulting
>>>Stonington, CT
>>>860.535.2080
>>>www.fpdc.com
>>>
>>>_______________________________________________
>>>Sprinklerforum mailing list
>>>[email protected]
>>>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>>
>>>For Technical Assistance, send an email to: [email protected]
>>>
>>>To Unsubscribe, send an email to:[email protected]
>>>(Put the word unsubscribe in the subject field)
>>>_______________________________________________
>>>Sprinklerforum mailing list
>>>[email protected]
>>>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>>
>>>For Technical Assistance, send an email to: [email protected]
>>>
>>>To Unsubscribe, send an email to:[email protected]
>>>(Put the word unsubscribe in the subject field)
>>>
>>>_______________________________________________
>>>Sprinklerforum mailing list
>>>[email protected]
>>>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>>
>>>For Technical Assistance, send an email to: [email protected]
>>>
>>>To Unsubscribe, send an email to:[email protected]
>>>(Put the word unsubscribe in the subject field)
>>>
>>>
>>>
>>>
>>>
>>>=======
>>>Email scanned by PC Tools - No viruses or spyware found.
>>>(Email Guard: 7.0.0.21, Virus/Spyware Database: 6.16220)
>>>http://www.pctools.com/
>>>=======
>>>
>>>
>>>
>>>
>>>
>>>=======
>>>Email scanned by PC Tools - No viruses or spyware found.
>>>(Email Guard: 7.0.0.21, Virus/Spyware Database: 6.16220)
>>>http://www.pctools.com/
>>>=======
>>>_______________________________________________
>>>Sprinklerforum mailing list
>>>[email protected]
>>>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>>
>>>For Technical Assistance, send an email to: [email protected]
>>>
>>>To Unsubscribe, send an email to:[email protected]
>>>(Put the word unsubscribe in the subject field)
>>
>> Todd G. Williams, PE
>> Fire Protection Design/Consulting
>> Stonington, CT
>> 860.535.2080
>> www.fpdc.com
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email to:[email protected]
>> (Put the word unsubscribe in the subject field)
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email to:[email protected]
>> (Put the word unsubscribe in the subject field)
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email to:[email protected]
>> (Put the word unsubscribe in the subject field)
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email to:[email protected]
>> (Put the word unsubscribe in the subject field)
>>
>
>
>
> --
> Ron Greenman
> Instructor
> Fire Protection Engineering Technology
> Bates Technical College
> 1101 So. Yakima Ave.
> Tacoma, WA 98405
>
> [email protected]
>
> http://www.bates.ctc.edu/fireprotection/
>
> 253.680.7346
> 253.576.9700 (cell)
>
> Member:
> AFSA, SFPE, ASCET, NFPA, NFSA, AFAA, ASEE, NIBS, WSAFM, WFC
>
> They are happy men whose natures sort with their vocations. -Francis
> Bacon, essayist, philosopher, and statesman (1561-1626)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
AFSA, SFPE, ASCET, NFPA, NFSA, AFAA, ASEE, NIBS, WSAFM, WFC

They are happy men whose natures sort with their vocations. -Francis
Bacon, essayist, philosopher, and statesman (1561-1626)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to