Are the city pumps redundant?   Will the water utilities and/or fire
department vouch for those pressures as normal operating conditions?
Most of San Diego County is relatively new (sub-50 years)
infrastructure, so this situation isn't unheard of around here.   In
checking with the water department, we have consistently found that
their position is that the pump system is regularly exercised, backed
up, and highly unlikely to fail.   Serving fire departments generally
concur.

To be on the safe side, take a 10% drop from static at your flow rate
and call it a day.

SL
 


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Brian
Harris
Sent: Tuesday, December 14, 2010 8:03 AM
To: [email protected]
Subject: Flow Test With City Pump

Just did a flow test for a new project and the static was 100psi, opened
the
hydrant and the residual dropped to 50psi for a couple of seconds and
then
the city pumps kicked on and the residual went to 110psi. When doing the
calc's for this system wouldn't you need to do it without the boost from
the
pumps? (S=100 R=50) If that is the case what do you do for the flow as
the
pitot reading was done after the pumps kicked in?

 

Brian Harris

First Defense Fire Protection

11957 Ramah Church Road

Huntersville, NC 28078

Phone: 704.948.3506

Fax: 704.948.3507

Nicet # 128476

 





=======
Email scanned by PC Tools - No viruses or spyware found.
(Email Guard: 7.0.0.21, Virus/Spyware Database: 6.16510)
http://www.pctools.com/
=======
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to