How big is each building?
If the total area for al the building is over 52,000-sq. ft., then this
is not acceptable.
However, if the total area is less than 52,000, then maybe it would be
okay, but I would need more info before making a decision...maybe.
rick matsuda
city of dallas

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of IPA
Sent: Tuesday, January 11, 2011 10:55 AM
To: sprinklerforum
Subject: One City Tap for Four Buildings

Hello,

I've got a project where there is only one tap into the city water
supply
and this tap supplies fire sprinkler systems for four buildings. The
only
problem is there is not one underground main which branches off to each
building underground. Instead the fire line goes into only one building
(building #1) with it's own riser, feeds the fire sprinklers system for
that
building then goes down the opposite side of the building, underground,
comes up into building #2, with it's own riser, feeds that fire
sprinkler
system then goes down underground and continues on to each building.
Each
building has it's own riser but if at anytime someone shuts down the
riser
at building #1 the entire complex goes down. I hope I made sense.

>From my perusal of 13 and 24 I didn't see anything that forbids this but
wanted to run it through the forum. It seems a little too wacky to me.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to