>  I had to flow heads in the pit, intake plenum, exhaust duct, etc. except the 
> mixing room when i used to design the spray booths for Blowtherm. That's what 
> the A.H.J. usually required. I was able to get a compromise with them 
> allowing me to use different orifice sizes in different areas of the booth so 
> as not to have to install a 6" riser for all the overage.
>
>
> George Medina Jr.
> Monterey Park, Ca
>
> -----Original Message-----
> From: Ron Greenman <[email protected]>
> To: sprinklerforum <[email protected]>
> Sent: Mon, Jan 10, 2011 2:05 pm
> Subject: Re: sprinklers in duct
>
>
> The duct or the spray booth? just figure all.
> On Mon, Jan 10, 2011 at 1:46 PM, Todd Williams <[email protected]> wrote:
>  OK, but there are two items that I have heard of, but can't find a reference
>  for: 1) the requirement for a sprinkler within 3 ft of the duct passing to
>  the outside, and 2) using pendent sprinklers in the vertical position on
>  vertical runs of duct.
>
>  Also, there is the nebulous statement "the water supply shall be sufficient
>  to supply all sprinklers likely to open in any one fire incident..." How
>  does one go about determining the number of sprinklers likely to open that
>  would be reasonable and satisfy the AHJ as well as the attorney for the
>  plaintiff?
>
>
>
>  At 03:49 PM 1/10/2011, you wrote:
>>
>> Or chapter 21 in NFPA 13
>>
>> Teresa M. King, S.E.T.
>> Design Manager
>> Front Range Fire Protection, Inc.
>> 4007 S. Lincoln Avenue, Suite 460
>> Loveland, CO  80537
>> ph. (970) 663-3310
>> fax (970) 663-7331
>>
>>
>>
>> -----Original Message-----
>> From: [email protected]
>> [mailto:[email protected]] On Behalf Of Dale Wingard
>> Sent: Monday, January 10, 2011 1:44 PM
>> To: [email protected]
>> Subject: RE: sprinklers in duct
>>
>> Try NFPA 33.  It is for Spray Application Using Flammables.
>>
>> Dale F. Wingard, SET
>> Design Manager
>> Triple "A" Fire Protection, Inc.
>> 251.649.2034
>> [email protected]
>>
>> -----Original Message-----
>> From: [email protected]
>> [mailto:[email protected]] On Behalf Of Todd
>> Williams
>> Sent: Monday, January 10, 2011 2:38 PM
>> To: [email protected]
>> Subject: sprinklers in duct
>>
>> I am doing a system for a spray booth and the associated exhaust
>> ducts. I can't seem to find the section of the NFPA standards that
>> references this. NFPA 91 says provide sprinkler protection without
>> any further guidance. NFPA 13 chapter 7 talks about cooking equipment
>> and it's ductwork, but doesn't give many specifics. Seems to me there
>> is something about having sprinklers within 3 ft of where the duct
>> exits the building, but I can't find it. Anybody know where this
>> stuff is off the top of their head?
>>
>> Todd G. Williams, PE
>> Fire Protection Design/Consulting
>> Stonington, CT
>> 860.535.2080
>> www.fpdc.com
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email
>> to:[email protected]
>> (Put the word unsubscribe in the subject field)
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email to:[email protected]
>> (Put the word unsubscribe in the subject field)
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email to:[email protected]
>> (Put the word unsubscribe in the subject field)
>
>  Todd G. Williams, PE
>  Fire Protection Design/Consulting
>  Stonington, CT
>  860.535.2080
>  www.fpdc.com
>
>  _______________________________________________
>  Sprinklerforum mailing list
>  [email protected]
>  http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>  For Technical Assistance, send an email to: [email protected]
>
>  To Unsubscribe, send an email to:[email protected]
>  (Put the word unsubscribe in the subject field)
>
>
> --
> on Greenman
> nstructor
> ire Protection Engineering Technology
> ates Technical College
> 101 So. Yakima Ave.
> acoma, WA 98405
> [email protected]
> http://www.bates.ctc.edu/fireprotection/
> 253.680.7346
> 53.576.9700 (cell)
> Member:
> FSA, SFPE, ASCET, NFPA, NFSA, AFAA, ASEE, NIBS, WSAFM, WFC
> They are happy men whose natures sort with their vocations. -Francis
> acon, essayist, philosopher, and statesman (1561-1626)
> ______________________________________________
> prinklerforum mailing list
> [email protected]
> ttp://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected]
> To Unsubscribe, send an email to:[email protected]
> Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
AFSA, SFPE, ASCET, NFPA, NFSA, AFAA, ASEE, NIBS, WSAFM, WFC

They are happy men whose natures sort with their vocations. -Francis
Bacon, essayist, philosopher, and statesman (1561-1626)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to