I agree with Matt's concept but would tweak the justification. Section 4.1.6 is a change of hazard that triggers a separate evaluation. I would not expect an owner (or inspector) to be able to identify or recognize adding such equipment to fall in this arena. I would fall back to 5.2.1.2 and say the inspector is suppose to identify violations to the clearance to deflector requirements.

Roland

On Jan 20, 2011, at 11:32 AM, Matthew J. Willis wrote:

I am surprised it is not a deluge....

If they were put in since last inspection, Yes code violation. (4.1.6)

If built that way, No. (1.1.2)



R/
Matt