John,

If I remember correctly, a "miss" by a code official does not mean the system 
is acceptable. The permit the contractor takes out at the beginning of the job 
requires that the system is installed by the referenced code that is adopted by 
the jurisdiction where the project is located and a variance to the code is 
required to be written on the AHJ's letterhead, if not the contractor is 
required to install by code. 

John you are correct in that "only time will tell if a violation results in an 
incident." Along with meeting someone's lawyer(s) 

Jim Davidson 
 
Davidson Associates 
Fire Protection * Medical Gas * Code Consulting  
302-994-9500   Fax:302-234-1781


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of John Drucker
Sent: Sunday, January 23, 2011 8:31 AM
To: [email protected]
Subject: RE: Rolling medical file storage

Violations have no concept of time. However only time will tell if a
violation results in an incident.

John Drucker, CET
Fire Protection Subcode Official 
Fire/Building/Electrical Inspector
Fire Marshals Office
Borough of Red Bank, NJ

Not the official position of any agency, association, committee or
otherwise.  Obtain required applications, permits, inspections and approvals
from Authority(s) Having Jurisdiction. 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of George Church
Sent: Saturday, January 22, 2011 2:26 PM
To: [email protected]
Subject: RE: Rolling medical file storage

A competitor claimed a finishing nail was an acceptable hanger because the
system had been inspected and accepted by the local BCO- who I hope didn't
walk the attic with his eyes closed and missed it.

So, its ok until time eternal (or a major renovation) if an inspector missed
an obvious code violation during the acceptance inspection & testing?

Like the system showing a static less than the demand at flow?
glc

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Thursday, January 20, 2011 2:46 PM
To: [email protected]
Subject: RE: Rolling medical file storage

Movable racks are supposed to be protected the same as multi-row racks.  So
based on the design there could be a violation.   But every questionable
system has always "been installed that way and accepted" by someone no one
can remember.



Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Matthew J.
Willis
Sent: Thursday, January 20, 2011 2:33 PM
To: [email protected]
Subject: RE: Rolling medical file storage

I am surprised it is not a deluge....

If they were put in since last inspection, Yes code violation. (4.1.6)

If built that way, No. (1.1.2)



R/
Matt

 

 

Matthew J. Willis, CET
Automatic Fire Sprinklers
Norred Fire Systems L.L.C.
318-387-1134 Voice
318-816-1087 Mobile
318-387-1163 Facsimile
[email protected]

> >-----Original Message-----
> >From: [email protected] [mailto:sprinklerforum-
> >[email protected]] On Behalf Of Gregg Key
> >Sent: Thursday, January 20, 2011 1:27 PM
> >To: [email protected]
> >Subject: Rolling medical file storage
> >
> >It has been a while since I have been on and I think this has been
> >discussed
> >before but cant find it in the archives so here I go.
> >
> >Doing a NFPA 25 inspection and find a medical storage room with rolling
> >files that are within 8" of the sprinklers. Sprinklers spaced 12x12. This
> >system has 8 rolling files and only room for 1 to be open at a time so no
> >way to get adequate coverage.  Was told it was installed like this from
> >beginning and was accepted. What sayest the Sprinkler forumites? code
> >violation or not? How would you address it? BTW this is at a State
> >facility.
> >Thanks
> >
> >C.Gregg Key, SET
> >Key Fire Protection Services,Inc
> >Project Manager
> >(O) 706-790-3473
> >(C) 706-220-8821
> >
> >_______________________________________________
> >Sprinklerforum mailing list
> >[email protected]
> >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> >For Technical Assistance, send an email to: [email protected]
> >
> >To Unsubscribe, send an email to:[email protected]
> >(Put the word unsubscribe in the subject field)
> >
> >No virus found in this incoming message.
> >Checked by AVG - www.avg.com
> >Version: 9.0.872 / Virus Database: 271.1.1/3375 - Release Date: 01/19/11
> >13:34:00

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to