NFPA 33 2011 9.4.6 Sprinklers systems protecting stacks or ducts shall meet all 
of the following requirements:
(1) Sprinklers shall be spaced no more than 12' apart.

Since the standard doesn't differentiate between vertical or horizontal duct 
then I interpret it to require sprinklers to spaced 12' on the vertical as well 
as horizontal.


Ryan Peterson
Wayne Automatic fire Sprinklers
407-877-5593

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of A.P.Silva
Sent: Tuesday, February 01, 2011 2:55 PM
To: [email protected]
Subject: Exhaust ducct

 
I normally provide one head at the top of a vertical exhaust stack coming
off a paint booth. The vertical duct is about 25 feet high. The booth
manufacturer says there should be two heads as maximum spacing on vertical
duct is 20 feet. Is this normal?

Tony