30% longer than if the water was right there, so the fire will be 30% bigger
and yes, more heads will open. For heads to operate faster you have to put
them closer to the fire, or closer to each other. The inequality comes from
the fact that in both the wet and dry case, they are both of those- same
spacing and height.  

-----Original Message-----
From: Ronl.Fletcher [mailto:[email protected]] 
Sent: Monday, February 07, 2011 12:53 PM
To: [email protected]
Subject: RE: a glaring inequality in 13?

30% longer than what, a wet system? I always thought the 30% increase was
because more heads are likely to open because of the delayed water delivery.

Ron Fletcher
Aero Automatic
Phoenix, AZ



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Brad
Casterline
Sent: Monday, February 07, 2011 11:42 AM
To: [email protected]
Subject: RE: a glaring inequality in 13?

Thanks Ken,
We increase the area 30% for dry because it takes the water 30% longer to
get to the head after it goes off. The inequality I see is in saying the
water will take 200 times longer to get to the head in the dry example,
since slope and response time based on height are equal in both cases. If I
was going to suggest something, it would be to add a 5th parameter to QR
Reduction- either "max slope = 2/12", or "wet, except dry is ok if
unoccupied attic not exceeding 20'". I prefer the latter, with my apologies
to Tyco :)
Thanks again! 

-----Original Message-----
From: ParsleyConsulting [mailto:[email protected]] 
Sent: Monday, February 07, 2011 12:23 PM
To: [email protected]
Subject: Re: a glaring inequality in 13?

Brad,

I'm not sure I see a "glaring inequality", since the allowable reduction 
for using quick response sprinklers would not apply to dry systems.

The increase in remote area for the pitch of the roof is applied equally 
to both wet and dry systems.

The increase for dry systems is only applied to dry systems [perhaps 
obviously].

The reduction for quick response sprinklers is not allowed for dry systems.

Are you suggesting that it should be?

PARSLEY CONSULTING
Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
[email protected] <mailto:[email protected]>e-mail
www.ParsleyConsulting.com <http://www.ParsleyConsulting.com>website


On 2/7/2011 9:50 AM, Brad Casterline wrote:
> I would appreciate thoughts and comments from all willing to take the
time:
>
> Combustible attic, 4/12 slope, 10' to peak. 1500*1.3=1950 for slope
exceeds
> 2/12. Light Hazard, so QR heads required. If DRY, 1950*1.3=2535. If WET,
> 1950*.6=1170. (QR Reduction). Doesn't this mean the area has to be
increased
> over 200% for DRY, not 30%? For 20' to the peak, 1950*.75=1463~~ 170%
> increase for DRY. Using SSU, the increase would be for the exact same
> spacing and height in both cases. BB and SD Attic heads 'increase' the
area
> 30% for DRY (from 5 to 7 heads), but without regard to height, and the
slope
> MUST be minimum 4/12. They must be within 6" each side of the peak, at 6'
> max. SSU also have to be within 6" each side, and 8' max is cheaper than a
> pump. I know this has not come up in the 16 months since I discovered the
> Forum. If it did before that, I would appreciate being pointed to the
> location of all discussion about it.
>
> Many thanks,
>
> Brad
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to