If you can't meet the restrictions for Specific application sprinklers, you would revert to Standard spray sprinkler or other listed sprinkler for use in concealed combustible spaces or attics. All the exclusions and exceptions in NFPA 13 would apply.
-----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Greg McGahan Sent: Tuesday, February 15, 2011 3:08 PM To: [email protected] Subject: COIN sprinklers OK, I have yet to find a space that fits the listing restrictions on wither make of these special sprinklers for flat concealed spaces... AND tech support doesn't seem to have the answers either.. We have one more similar space - 1 on 12 pitch, 2 x 12 joists at the roof BUT there are girder trusses about 18" wide spaced approx. 16'-0 on center that create spaces 18" wide x 56' long that are well over 36" deep. The peak is also 37" clear between the bottom of joists to the top of the ceiling. It doesn't fit in the box, and the Owner has no money to provide draft stops as required by the listing.... What do we do?? -- Greg McGahan Living Water Fire Protection, LLC 1160 McKenzie Road Cantonment, FL 32533 850-937-1850 fax 850-937-1852 _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)