Greg, I had a very similar project a few years back.  The 'shallow' end of
the combustible concealed space was less than 36" deep (thus REQUIRED to be
protected by COINs or equals) and the 'deep' end was greater than 36" deep
(thus NOT ALLOWED to be protected by COINs or equal). The owner didn't like
it, but we told him to either install draft stops to separate the COINS and
QR's, or hire an FPE to sign-off on an equivalent design. 

I feel your pain.

Ed Kramer
Littleton, CO