See NFPA 25 Chapter 15.  This covers pre-planned impairments and requires a 
coordinator that has been given authority to make decisions on the owner's 
behalf.  It also requires the coordinator to notify all involved parties (ie. 
AHJ, insurers, fire dept, etc) and locate impairment tags throughout.

Duane Johnson, PE
Program Manager
Division of the Fire Marshal (Support Contractor)
Office of Research Services 
National Institutes of Health 
301-496-0487

"Protecting Science - One Sprinkler at a Time"


-----Original Message-----
From: Joe Burtell [mailto:[email protected]] 
Sent: Monday, March 07, 2011 11:40 AM
To: [email protected]
Subject: RE: Decommissioning a system

IFC
901.6 Inspection, testing and maintenance.
Fire detection, alarm and extinguishing systems shall be maintained in an
operative condition at all times, and shall be replaced or repaired where
defective. Nonrequired fire protection systems and equipment shall be
inspected, tested and maintained or removed.


Pay attention to the Last sentence, REMOVED.
Joe Burtell


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Thom
Sent: Monday, March 07, 2011 9:32 AM
To: [email protected]
Subject: RE: Decommissioning a system

We would use IBC 3303, as our basic guide to de-commission (Demolition) of
any system which requires the AHJ to provide (3303.6) "---In accordance with
the approved rules and requirements of the authority having jurisdiction."

I would caution you that leaving sprinkler heads in place that no longer
operate, in an "Occupied" building gives the false sense of protection,
similar to just gluing heads to a ceiling without and pipe supplying them. I
don't know how "Litigious" the Irish court system is in regard to "Public
safety" but Old English law can't be much different than here, except that
you have far fewer lawyers.

I'd remove anything that say's or looks like a fire protection system,
including heads, riser, FDC, signs and pipe if possible, but the AHJ should
supply you with written guidelines for your files.

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Damien
Shannon
Sent: Monday, March 07, 2011 4:39 AM
To: [email protected]
Subject: Decommissioning a system

Dear Forum,
 
I was wondering if there is a Standard or Datasheet that people are aware of
for decommissioning a system.
We are requested to decommission a few buildings here. Some are remaining
open, some are closing. Some will be heated but some are not. 
One of my big concerns is that in some cases there are drywall/plaster
ceilings, with drops to the heads. Therefore there will be water in the
drops. Since the system would be left such that it would not be a sealed
system, thereby allowing room for expansion during freeze periods, would
there still be cause for concern of breakage/leakage?
Some of the areas would be very difficult to remove every sprinkler (with
severe floor obstructions.), and there may be areas with certain amount of
misc trapped water. 
Has anyone got experience in this regards, or is there a Standard to be
followed.
Any help would be appreciated.
 
BTW, I recently closed QED Sprinkler Designs to take a position back in the
'Homeland' with my Father's Company. (Believe we just became the first Irish
AFSA memberJ). I had mentioned this move to a few of you before but there
have been a few postponed starts which has led me to be in limbo for a while
there. 
Thank you all for your help and encouragement while I was State side (it was
a very special 16 years for me), and hope to keep in touch. 
 
Damien Shannon
Provincial Sprinkler Company Ltd.
Unit 4, Cork Airport Industrial Estate
Kinsale Road,
Cork, Ireland.
Tel: (021) 4965058
Fax: (021) 4317425
 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to