Matt,

As an example the space between a suspended ceiling and the floor above is
often considered an interstitial space. 

Frankly as an AHJ if an Architect wants the Interstitials sprinklered
without consideration of NFPA-13's special situations, no argument here.

Perhaps these code references will help.

2006 / 2009 IBC

709.4 / 710.4 Continuity.

Smoke barriers shall form an effective membrane continuous from outside wall
to outside wall and from the top of the foundation or floor/ceiling assembly
below to the underside of the floor or roof sheathing, deck or slab above,
including continuity through concealed spaces, such as those found above
suspended ceilings, and interstitial structural and mechanical spaces. The
supporting construction shall be protected to afford the required
fire-resistance rating of the wall or floor supported in buildings of other
than Type IIB, IIIB or VB construction.

Exception: Smoke-barrier walls are not required in interstitial spaces where
such spaces are designed and constructed with ceilings that provide
resistance to the passage of fire and smoke equivalent to that provided by
the smoke-barrier walls.

2009 NFPA-5000

Table of Contents; Interstitial spaces . . . . . . . . . . . . . . . . . . .
. . . . . . . . . . . . . . . .see Concealed spaces

7.4.3.3.1 Interstitial spaces used solely for building or process systems
directly related to the level above or below shall not be considered a
separate story.

2010 NFPA-72 A.8.15.1.2.1 

Minor quantities of combustible materials such as but not limited to:
cabling, nonmetallic plumbing piping, non-structural wood, etc. can be
present in concealed spaces constructed of limited or noncombustible
materials but should not typically be viewed as requiring sprinklers (see
8.15.1.1). For example, it is not the intent of this section to require
sprinklers, which would not otherwise be required, in the interstitial space
of a typical office building solely due to
the presence of the usual amount of cabling within the space. The threshold
value at which sprinklers become necessary in the concealed space is not
defined.

John Drucker, CET
Fire Protection Subcode Official 
Fire/Building/Electrical Inspector
Fire Marshals Office
Borough of Red Bank, NJ

Not the official position of any agency, association, committee or
otherwise.  Obtain required applications, permits, inspections and approvals
from Authority(s) Having Jurisdiction. 



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Martin,
Matthew
Sent: Monday, March 07, 2011 1:39 PM
To: [email protected]
Subject: Interstitial Space

   Can anyone tell me what the NFPA says about the requirements of
sprinklers in the interstitial space. What is the definition of "
Interstitial Space"?
 Also where in the NFPA is the term Interstitial Space used.
 We have an Architect who says that a fully sprinklered building includes
sprinklers in all the interstitial spaces.

 Thanks in advance,



Matthew Martin
CQC Manager
Suffolk Construction Company, Inc.
Direct: 323-781-1778
Cell: 949-892-7419

www.suffolkconstruction.com

Please consider the environment before printing this e-mail
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to