If you end up with "HERE'S THE EXTRA YOU OWE US" then yes, you're on the right 
track. 
Might be you owe em a credit from the FA guy for the detectors not installed, 
but I'll bet the SSU were a lot more.

Taking their everywhere and completely would have you providing sprinklers 16" 
on center above all the wall cavities formed by vertical metal studs, inside 
all the ductwork, and in California- I can't even render a guess as to what 
other cavities might require protection.

George Church
Rowe Sprinkler Systems, Inc.
PO Box 407, Middleburg, PA 17842
877-324-ROWE       570-837-6335 fax
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Martin, Matthew
Sent: Monday, March 07, 2011 2:41 PM
To: [email protected]
Subject: RE: Interstitial Space

Thank you for all the answers so far.  Here is some further clarifications.
 Our project is a new high school in Los Angeles , CA.
 The buildings in question are 4 story classroom buildings with the space 
between floors of about 36"-40" of non combustible space.
The argument we are having is that the upright sprinklers are not required 
based on NFPA 8.14.1.2 (2002). Many of you have confirmed our argument, thank 
you. The design team directed us to install them about eight months ago and 
planned on paying us for the work. Now they are saying they were required 
because fully means "everywhere and completely." Part of my argument back will 
be that they wanted the upright sprinklers installed in lieu of heat detectors. 
It is heat detectors that are required for activation of the fire alarm system. 
The sprinkler system ( uprights) here is not being used as a suppression system 
but as an activation system. Am I on the right track?



Matthew Martin
CQC Manager
Suffolk Construction Company, Inc.
Direct: 323-781-1778
Cell: 949-892-7419

www.suffolkconstruction.com

Please consider the environment before printing this e-mail-----Original 
Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of George Church
Sent: Monday, March 07, 2011 11:23 AM
To: [email protected]
Subject: RE: Interstitial Space

Clearly there's a HUGE dif between an interstitial space above a drop ceiling 
and below the deck above, and the vision you made me remember of an animal 
research lab at Merck with 15' high interstitial spaces with grated floors 
throughout. In that one, sprinklers were installed in the noncombustible 
concealed space because with the doorways accessing the grated platform, it was 
no longer concealed.

Another point to consider when dealing with pharmaceuticals, clean rooms, bio 
and nanotechnologies, is the dollar values involved (or business interruption) 
may cause an Owner or insurance carrier to ask for sprinkler protection beyond 
that required by minimum consensus standards.

George Church
Rowe Sprinkler Systems, Inc.
PO Box 407, Middleburg, PA 17842
877-324-ROWE       570-837-6335 fax
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Monday, March 07, 2011 2:11 PM
To: [email protected]
Subject: Re: Interstitial Space

For many industrial projects, especial biotech and microelectronics, 
interstitial space is commonly used to describe the space between floors - 
especially where the spaces are tall enough to accommodate personnel.

I am now gun shy enough to where I plan full automatic sprinkler protection 
throughout interstitial spaces.  We once got burned where the local AHJ's 
signed off in writing that the interstitial spaces did not have to be 
sprinklered only to be told a year later that they would require protection 
based on a new evaluation by a code consultant.  We had been told that minimal 
plastic drain pipe and fire resistant cable was acceptable.

If the interstitial "floor" is a walkable ceiling, you will more than likely 
lose the battle even if the space is non-combustible and has non-combustible 
contents because the argument will be that storage would be possible.

Regards,

Jim


James L (Jim) Roberts, PE/SET |FLUOR|Central Operations| 
[email protected]|IODC 20.5149 |864.281.5149| www.fluor.com



From:       Todd Williams <[email protected]>
To:         [email protected]
Date:       03/07/2011 01:49 PM
Subject:    Re: Interstitial Space
Sent by:    [email protected]



Interstitial and concealed can be assumed synonymous in our situation. 
Interstitial tends to apply more to things like spaces between walls.


At 01:46 PM 3/7/2011, you wrote:
>Is the space combustible?
>On Mar 7, 2011 12:39 PM, "Martin, Matthew"
<[email protected]>
>wrote:
> > Can anyone tell me what the NFPA says about the requirements of
sprinklers
>in the interstitial space. What is the definition of " Interstitial
Space"?
> > Also where in the NFPA is the term Interstitial Space used.
> > We have an Architect who says that a fully sprinklered building
includes
>sprinklers in all the interstitial spaces.
> >
> > Thanks in advance,
> >
> >
> >
> > Matthew Martin
> > CQC Manager
> > Suffolk Construction Company, Inc.
> > Direct: 323-781-1778
> > Cell: 949-892-7419
> >
> > www.suffolkconstruction.com
> >
> > Please consider the environment before printing this e-mail 
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > For Technical Assistance, send an email to:
> > [email protected]
> >
> > To Unsubscribe, send an email
to:[email protected]
> > (Put the word unsubscribe in the subject field)
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email
>to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)


------------------------------------------------------------
The information transmitted is intended only for the person or entity to which 
it is addressed and may contain proprietary, business-confidential and/or 
privileged material.
If you are not the intended recipient of this message you are hereby notified 
that any use, review, retransmission, dissemination, distribution, reproduction 
or any action taken in reliance upon this message is prohibited. If you 
received this in error, please contact the sender and delete the material from 
any computer.

Any views expressed in this message are those of the individual sender and may 
not necessarily reflect the views of the company.
------------------------------------------------------------

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field) 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field) 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to