Mark - I haven't had to deal with this section before, but I can see the ambiguity. It seems unclear if they are talking about the area of a warehouse sprinkler system or the actual size of a warehouse fire area (i.e. construction of the warehouse vs construction of the sprinkler system).
But I'll go out on a limb and suggest that they are discussing the size limitation of the warehouse fire areas. I.e., if you have a warehouse greater than 60,000 sq.ft., then you need to add a fire separation wall to create areas of less than 60,000 sq.ft. As an alternative, you can go up to 120,000 sq.ft. in the warehouse fire area if you follow the guidelines mentioned: increase sprinkler system design areas; provide enough isolation valves on the underground loop around the warehouse (as applicable); and provide a secondary fire pump if one pump is required. Of course, the third interpretation is that you cannot have more than 60,000 sq.ft. of warehouse in one building. The exception being that you can have 120,000 sq.ft. max. if you follow the guidelines above. But I don't think that's the intent. Mark A. Sornsin, PE| Fire Protection Engineer Ulteig Engineers, Inc.| Fargo, ND [email protected] -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Mark.Phelps Sent: Monday, March 21, 2011 4:23 PM To: [email protected] Subject: RE:UFC 6-11.4 Can anyone shed any light on the meaning of this section in the UFC? Bill? Anyone? Mark at Aero -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Eric Tysinger Sent: Monday, March 21, 2011 12:37 PM To: [email protected] Subject: RE: I have used a single 2½" female hose x male thread adapter, about a foot off the floor. Then you use a short piece of 2½" fire hose for testing. Thanks, Eric Tysinger CET NICET III - 108988 Designer Wayne Automatic Fire Sprinklers, Inc. 4370 Motorsport Drive Concord, NC 28027 p: (704)782-3032 x1751 f: (704)795-6838 C: (239)633-9703 -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Todd Williams Sent: Monday, March 21, 2011 3:06 PM To: [email protected] Subject: Tom, Do you have a picture or a sketch of a drain riser and connections for a 2-1/2" pressure reducing hose valve? I'm having a hard time picturing how this all goes together. Also any hints on distance or arrangement would be helpful. Thanks Todd Todd G. Williams, PE Fire Protection Design/Consulting Stonington, CT 860.535.2080 www.fpdc.com _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)