I don't think Mark is too far out on that limb.

On Mon, Mar 21, 2011 at 2:54 PM, Mark Sornsin <[email protected]> wrote:
> Mark - I haven't had to deal with this section before, but I can see the 
> ambiguity. It seems unclear if they are talking about the area of a warehouse 
> sprinkler system or the actual size of a warehouse fire area (i.e. 
> construction of the warehouse vs construction of the sprinkler system).
>
> But I'll go out on a limb and suggest that they are discussing the size 
> limitation of the warehouse fire areas. I.e., if you have a warehouse greater 
> than 60,000 sq.ft., then you need to add a fire separation wall to create 
> areas of less than 60,000 sq.ft. As an alternative, you can go up to 120,000 
> sq.ft. in the warehouse fire area if you follow the guidelines mentioned: 
> increase sprinkler system design areas; provide enough isolation valves on 
> the underground loop around the warehouse (as applicable); and provide a 
> secondary fire pump if one pump is required.
>
> Of course, the third interpretation is that you cannot have more than 60,000 
> sq.ft. of warehouse in one building. The exception being that you can have 
> 120,000 sq.ft. max. if you follow the guidelines above. But I don't think 
> that's the intent.
>
> Mark A. Sornsin, PE| Fire Protection Engineer
> Ulteig Engineers, Inc.| Fargo, ND
> [email protected]
>
>
> -----Original Message-----
> From: [email protected] 
> [mailto:[email protected]] On Behalf Of Mark.Phelps
> Sent: Monday, March 21, 2011 4:23 PM
> To: [email protected]
> Subject: RE:UFC 6-11.4
>
> Can anyone shed any light on the meaning of this section in the UFC? Bill? 
> Anyone?
> Mark at Aero
>
>
> -----Original Message-----
> From: [email protected] 
> [mailto:[email protected]] On Behalf Of Eric Tysinger
> Sent: Monday, March 21, 2011 12:37 PM
> To: [email protected]
> Subject: RE:
>
> I have used a single 2½" female hose x male thread adapter, about a foot off 
> the floor. Then you use a short piece of 2½" fire hose for testing.
>
>
> Thanks,
> Eric Tysinger CET
> NICET III - 108988
> Designer
> Wayne Automatic Fire Sprinklers, Inc.
> 4370 Motorsport Drive
> Concord, NC 28027
> p: (704)782-3032 x1751
> f: (704)795-6838
> C: (239)633-9703
>
> -----Original Message-----
> From: [email protected] 
> [mailto:[email protected]] On Behalf Of Todd Williams
> Sent: Monday, March 21, 2011 3:06 PM
> To: [email protected]
> Subject:
>
> Tom,
>
> Do you have a picture or a sketch of a drain riser and connections for a 
> 2-1/2" pressure reducing hose valve? I'm having a hard time picturing how 
> this all goes together. Also any hints on distance or arrangement would be 
> helpful. Thanks
>
> Todd
>
> Todd G. Williams, PE
> Fire Protection Design/Consulting
> Stonington, CT
> 860.535.2080
> www.fpdc.com
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field) 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field) 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC

They are happy men whose natures sort with their vocations. -Francis
Bacon, essayist, philosopher, and statesman (1561-1626)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to