I don't believe there is a requirement either way.  But I personally think it 
best to locate the check valve as close to the FDC as possible (without getting 
into freezing problems). It's got to be easier on the system if it is ever 
charged by the fire department; and it gives a degree of supervision of the 
pipe between the check valve and the riser (in for form of dripping water if a 
leak were to occur).

Mark A. Sornsin, PE| Fire Protection Engineer 
Ulteig Engineers, Inc.| Fargo, ND  
[email protected] 



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Dewayne Martinez
Sent: Tuesday, April 05, 2011 3:18 PM
To: [email protected]
Subject: Check valve location on a long FDC run

For a riser with a long bulk run to the FDC location is it better to locate the 
check valve by the riser or by the remote FDC?
 
Thanks,
Dewayne   