If the system is expected to be in accordance with a newer edition of NFPA 14, 
it is required that any sprinkler connection to a standpipe be furnished with a 
shut-off valve; if it's in accordance with 2003 or later it has to be a control 
valve and a check valve.   Not necessarily a full floor control, but a 
sectional shutoff at least.

SML



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Thursday, April 21, 2011 2:20 PM
To: [email protected]
Subject: RE: Combination standpipe riser & hose flows

No, they would be of no value.

Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Ronl.Fletcher
Sent: Thursday, April 21, 2011 5:17 PM
To: [email protected]
Subject: RE: Combination standpipe riser & hose flows

Automatic dry combination standpipe? Do you have a floor control assembly for 
the sprinkler system on each level?


Ron Fletcher
Aero Automatic
Phoenix, AZ




-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Thursday, April 21, 2011 1:43 PM
To: [email protected]
Subject: RE: Combination standpipe riser & hose flows

So if I'm clear on this,you have a combination dry automatic standpipe 
that also feeds the dry sprinkler system,all on the same system?

Lamar Vaughn,SET


On Thu, Apr 21, 2011 at 4:29 PM, [email protected] wrote:

> The Class I's work by themselves.
>
> But I do have all of this on one common riser.
> If I add the most remote 1.5" hose reel at 65 psi and 50 gpm to the 
> sprinkler demand, I'm 12 lbs over my available.
>
> Craig L. Prahl, CET   Fire Protection CH2MHILL
> Lockwood Greene
> 1500 International Drive
> Spartanburg, SC  29304-0491
> Direct - 864.599.4102
> Fax - 864.599.8439
> CH2MHILL Extension  74102
> [email protected]
>
>
>
> -----Original Message-----
> From: [email protected] 
> [mailto:[email protected]] On Behalf Of Steve 
> Leyton
> Sent: Thursday, April 21, 2011 4:25 PM
> To: [email protected]
> Subject: RE: Combination standpipe riser & hose flows
>
> That sounds okay to me.  If you can make the Class I's work, then the 
> Class II's should as well, eh?
>
> SML
>
>
>
> -----Original Message-----
> From: [email protected] 
> [mailto:[email protected]] On Behalf Of 
> [email protected]
> Sent: Thursday, April 21, 2011 1:09 PM
> To: [email protected]
> Subject: RE: Combination standpipe riser & hose flows
>
> Not considered a high rise.  Supply is automatic.
>
> I've calc'd the standpipe alone and can make it work from the 
> automatic source (fire pumps from 1MM gallon on-site storage water 
> tank)
>
> I can make the sprinklers by themselves work from the same source.
>
> It's just if they are put together that it won't work.  Not enough 
> pressure.
>
> Craig L. Prahl, CET   Fire Protection CH2MHILL
> Lockwood Greene
> 1500 International Drive
> Spartanburg, SC  29304-0491
> Direct - 864.599.4102
> Fax - 864.599.8439
> CH2MHILL Extension  74102
> [email protected]
>
>
>
> -----Original Message-----
> From: [email protected] 
> [mailto:[email protected]] On Behalf Of Steve 
> Leyton
> Sent: Thursday, April 21, 2011 4:03 PM
> To: [email protected]; [email protected]
> Subject: RE: Combination standpipe riser & hose flows
>
> Is the building considered a high-rise?   Is the Class I standpipe 
> system an automatic or manual water supply?
> The collective intent of 13 and 14 is that you have to hydraulically 
> prove the most demanding condition(s) of the sprinkler and standpipe 
> systems individually, but not concurrently.   So if you're 
> hydraulically calculating the Class I standpipe component you need to 
> know if you're calculating from the automatic source or the FDC 
> (manual system).   To add Class II components, you will have to do an 
> automatic calculation in accordance with 14.   For the sprinklers, you 
> would design hydraulically per 13.    Contrary to popular practice, 
> you don't have to take an inside hose when you have a sprinkler 
> system, only when you have hose valves supplied by a sprinkler system 
> that are not considered a standpipe system.
>
> The foregoing is my opinion only and does not necessarily represent 
> the opinion or intent of the NFPA 14 Technical Committee on Standpipe 
> and Hose Systems.
>
> Steve Leyton
> Protection Design & Consulting
> San Diego, CA
>
> -----Original Message-----
> From: [email protected] 
> [mailto:[email protected]] On Behalf Of 
> [email protected]
> Sent: Thursday, April 21, 2011 12:56 PM
> To: [email protected]; [email protected]
> Subject: Combination standpipe riser & hose flows
>
> Admittedly I'm kind of at an impasse.
> I've got a 4 level open process structure.  Top level is about 85ft 
> above grade.  Non-occupied.  The structure is provided with a dry 
> sprinkler system and has 2.5" hose outlets at intermediate landings. 
> The owner has requested 1.5" hose reels at each floor for their 
> responders.
> The area of the upper floor is only about 1400 sq. ft.  Due to 
> obstructions and some equipment that requires impingment protection 
> the number of heads flowing is about 33.
>
> The structure is fully sprinklered.
>
> When calculating the sprinkler flow I'm trying to decipher the text in 
> NFPA 13 and 14 (2010) concerning how to include or not, the flow and 
> pressure required for the 2.5" hose connections.
>
> If I flow 500 gpm through the top two 2.5" valves I'm good.
>
> If I have to provide for 250 gpm in addition to the sprinkler flow I'm 
> good.
>
> Where I'm in the toilet is if I have to provide that 2.5" valve at 250 
> gpm AND at 100 psi.
> 13 makes it sound like I don't have to include the hose flow if my 
> sprinkler flow is the higher value NFPA 13-2010 12.8.5(2) but this is 
> referring to wet system, no reference to dry systems.
> But if that is true, and I don't have to include the extra hose flow, 
> do I still need to provide 100 psi at that outlet?
> Am I missing something here?
>
> Is it assumed there will be simultaneous flow of the 2.5" hose AND 
> sprinklers?
>
>
> Craig L. Prahl, CET   Fire Protection CH2MHILL
> Lockwood Greene
> 1500 International Drive
> Spartanburg, SC  29304-0491
> Direct - 864.599.4102
> Fax - 864.599.8439
> CH2MHILL Extension  74102
> [email protected]
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]
> (Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to