So you're not using 13R?
If 13R is applicable, then there's a 30 minute duration.

If the storage means you can't use 13R since it isn't incidental to the 
residential nature of the building, then you are 13 and an hour.
I've seen plenty of commercial storage areas that are OH1- read the def in 13.

George L.  Church, Jr., CET  
Rowe Sprinkler Systems, Inc.
PO Box 407, Middleburg, PA 17842
877-324-ROWE       570-837-6335 fax
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Joel Chaim
Sent: Tuesday, June 07, 2011 3:37 PM
To: [email protected]
Subject: RE: Attic storage design on a 13R system 

The attic space is almost as big as the livable space and they store up there 
all kinds of stuff. They store more just then house stuff.

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of George Church
Sent: Tuesday, June 07, 2011 12:45 PM
To: [email protected]
Subject: RE: Attic storage design on a 13R system 

Where do you see NFPA 13R, your installation standard, requiring 60 minutes?
Mine says 30 minute duration. 

ONLY a few items come over from 13 when outside the dwelling unit.
Don't believe duration, hose streams, protection of combustible interstitial 
spaces and a host of other 13 requirements apply.

Remember you're designing to 13R. Stop thinking 13 (in its entirety) applies 
when you go outside the dwelling unit cause it don't.


George L.  Church, Jr., CET
Rowe Sprinkler Systems, Inc.
PO Box 407, Middleburg, PA 17842
877-324-ROWE       570-837-6335 fax
[email protected]



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Joel Chaim
Sent: Tuesday, June 07, 2011 11:36 AM
To: [email protected]
Subject: RE: Attic storage design on a 13R system 

But if we call it OH I, than we need 60 minutes that's my real problem.

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of George Church
Sent: Tuesday, June 07, 2011 9:54 AM
To: [email protected]
Subject: RE: Attic storage design on a 13R system 

Whoa!
Where does the 60 minute water duration come from?
It's not brought in from #13 on that short list that I see. 
So you need the appropriate density for the 13R water supply duration- Don't 
need no stinkin hose allowance in 13R And you may be able to call the storage 
area OH 1 and .15.


George L.  Church, Jr., CET
Rowe Sprinkler Systems, Inc.
PO Box 407, Middleburg, PA 17842
877-324-ROWE       570-837-6335 fax
[email protected]



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Mark Sornsin
Sent: Monday, June 06, 2011 4:31 PM
To: [email protected]
Subject: RE: Attic storage design on a 13R system 

Joel: It appears the first caveat is the biggest as far as reducing demand.
Is the attic going to be 500 sq.ft. or less, or will it be subdivided that way? 
If so it appears you can have 4 heads at 0.2 density. At 60 minutes that should 
keep you below 7,500 gallons, depending on the efficiency of the system (lack 
of overage).

Mark A. Sornsin, PE| Fire Protection Engineer Ulteig Engineers, Inc.| Fargo, ND 
[email protected] 



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Joel Chaim
Sent: Monday, June 06, 2011 11:56 AM
To: [email protected]
Subject: Attic storage design on a 13R system 

I have a small building that's 3000 sq. feet designed as per NFPA 13R. but they 
want to use the attic for a storage room and the water supply is a tank and 
they need more water because the storage classification brings it up to
60 min.

 

My question is does this section of the code do any good and reduce the water 
duration requirement? 

 

6.7.2.2  The system demand of areas outside the dwelling unit shall be 
permitted to be limited to the number of sprinklers in the compartmented area 
but shall not be greater than the demand for a total of four sprinklers where 
all of the following conditions are met: 

(1)          The area is compartmented into areas of 500 ft2 (46 m2) or less
by 30-minute fire-rated construction.

(2)          The area is protected by quick-response or residential
sprinklers not exceeding 130 ft2 (12 m2) per sprinkler for ordinary hazard,
225 ft2 (20.9 m2) for light hazard, or the allowable coverage of the sprinkler 
listing.

(3)          Openings have a lintel at least 8 in. (203 mm) in depth.

(4)          The total area of openings does not exceed 50 ft2 (4.6 m2) for
each compartment.

(5)          Discharge densities are in accordance with  NFPA 13, Standard
for the Installation of Sprinkler Systems.

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field) 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field) 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
-----
No virus found in this message.
Checked by AVG - www.avg.com
Version: 10.0.1382 / Virus Database: 1511/3684 - Release Date: 06/06/11

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field) 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
-----
No virus found in this message.
Checked by AVG - www.avg.com
Version: 10.0.1382 / Virus Database: 1511/3686 - Release Date: 06/07/11

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to