Charles, here ya go.

NJ Uniform Fire Code - Subchapter 4 - Applies to Pre-UCC buildings,
typically pre 1977.  Is that what your're looking for ?

N.J.A.C. 5:70-4.7     Fire suppression systems

 (h) In all buildings, any windowless basement or story located below
the seventh story shall be equipped throughout with an automatic fire
suppression system installed in accordance with the New Jersey Uniform
Construction Code.
  
1. Stories or basements shall not be considered windowless when there is
provided on at least one side of such story or basement fire fighter
access through openings, such as windows, doors or access panels, that
are located entirely above the adjoining grade level.
  
2. Such openings shall be at least:
  
i. 32 inches by 48 inches in size, spaced not more than 100 feet apart
in each story or basement; or
ii. 22 inches by 42 inches in size, spaced not more than 30 feet apart
in each story or basement.

3. All openings for fire fighter access shall conform to all the
following:

i. Openings shall be unobstructed to allow fire fighting and rescue
operations from the exterior; and
ii. Openings in stories at or above grade shall have a sill height of
not more than 36 inches as measured from the finished floor level.
Openings in basements shall have no sill height restrictions; and
iii. Openings shall be readily identifiable and openable from the
outside or shall be glazed with plain flat glass.

4. When openings in a story are provided on only one side and the
opposite wall of such story is more than 75 feet from such openings, the
story shall be considered windowless unless openings as specified above
are provided on at least two sides of the exterior walls of the story.
  
5. If any portion of a basement is located more than 75 feet from
openings as specified above, the basement shall be considered
windowless.

6. Windowless basements not exceeding 3,000 square feet in area shall be
exempt from this automatic suppression requirement, provided a
supervised automatic fire alarm system shall be installed in accordance
with the New Jersey Uniform Construction Code.

7. In windowless basements greater than 3,000 square feet, but not
exceeding 10,000 square feet in area, the required suppression system
need not be connected to a water supply other than an existing domestic
supply if the following conditions are met:

i. The suppression system shall be provided with a fire department
connection, which shall be marked with a sign reading "Basement Area
Sprinkler Water Supply"; and
ii. A supervised automatic fire alarm system shall be installed in
accordance with the New Jersey Uniform Construction Code.
  

Hope this helps,

John Drucker Jr CET
Fire Protection Subcode Official
Fire/Building/Electrical Inspector
Borough of Red Bank, NJ  
 
  

> Thanks for the IBC (NJ) code reference(s), but I think I'm looking for

> a specific NJ code on "windowless basements" which I believe has  
> exceptions to the exceptions.
>
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)


CONFIDENTIAL AND PROPRIETARY:
This email message is intended only for the use of the individual or entity to 
which it is addressed and may contain information that is privileged and 
confidential, nor is it, unless specifically stated, intended to be relied upon 
by any person or persons other than the individual or entity named above and no 
warranties or representations are made or intended to persons or entities not 
named above.  If the reader is not the intended recipient, you are hereby 
notified that any dissemination, distribution or copying of this communication 
is strictly prohibited.  If you have received this communication in error, 
please notify us immediately by telephone, return this message to the address 
above and delete all copies.  Thank you.

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to