And for those that might not completely understand (like me), how do we take
this type of MSDS info and extropolate it into a design? Can you give me a
gentle poke in the right direction.

Richard

On Tue, Jul 19, 2011 at 3:40 PM, Thom <[email protected]> wrote:

> http://www.sciencelab.com/msds.php?msdsId=9924458
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Dewayne
> Martinez
> Sent: Tuesday, July 19, 2011 1:12 PM
> To: [email protected]
> Subject: Commodity classification of Lard
>
> Anyone know what the commodity classification of animal fat lard would
> be?  I didn't see anything in NFPA or FM on this after a quick review.
> I have a refrigerated storage area with wood pallets containing 64 - 50
> lbs blocks of lard in which each block is placed in a plastic bag and
> enclosed in corrugated cardboard box.
> Thanks,
>
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to