The MSDS cited is for Lard Oil, which may behave differently than solid blocks 
of Lard. Need to fully research. Refer back to my comment about it being the 
PE's job to evaluate.

Now if you bought "I Can't Believe It's Not Lard"......


At 05:12 PM 7/19/2011, you wrote:
>Looking at the MSDS, it has a Flash Point of 419-deg. F (215 deg C), and
>could be considered a combustible liquid subject to NFPA 30, even though it
>is stored in solid form. I would also look at butter or margarine as
>possible comparables, and also vegetable oil.
>
>My opinion is that this would be classified as a Class IIIB Liquid in NFPA
>30.
>
>
>
>Jeff Hewitt, PE, SET, SFPE (Professional Member)
>Corporate Engineer
>Bi-State Fire Protection Corporation
>
>241 Hughes Lane
>St. Charles, MO  63301
>636-946-0011
>636-946-5172 (fax)
>314-574-6989 (cell)
>
>Fire Sprinklers Save lives.
>Can You Live Without Them?
>
>-----Original Message-----
>From: [email protected]
>[mailto:[email protected]] On Behalf Of Richard
>Lindner
>Sent: Tuesday, July 19, 2011 3:58 PM
>To: [email protected]
>Subject: Re: Commodity classification of Lard
>
>And for those that might not completely understand (like me), how do we take
>this type of MSDS info and extropolate it into a design? Can you give me a
>gentle poke in the right direction.
>
>Richard
>
>On Tue, Jul 19, 2011 at 3:40 PM, Thom <[email protected]> wrote:
>
>> http://www.sciencelab.com/msds.php?msdsId=9924458
>>
>>
>> -----Original Message-----
>> From: [email protected]
>> [mailto:[email protected]] On Behalf Of Dewayne
>> Martinez
>> Sent: Tuesday, July 19, 2011 1:12 PM
>> To: [email protected]
>> Subject: Commodity classification of Lard
>>
>> Anyone know what the commodity classification of animal fat lard would
>> be?  I didn't see anything in NFPA or FM on this after a quick review.
>> I have a refrigerated storage area with wood pallets containing 64 - 50
>> lbs blocks of lard in which each block is placed in a plastic bag and
>> enclosed in corrugated cardboard box.
>> Thanks,
>>
>>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to