We've got a school up here with a placard that says that BoR pressure is 7.5 
psi.

Also, a couple of years ago, I worked on a revision to a system with a placard 
on the riser. When I checked the calc for the old demand, I found that the 
placard was off by over 100 psi (rounded). 


At 04:32 PM 7/19/2011, you wrote:
>Not that unusual for multiple placards.
>One MRA might need a hi pres w/low flow.
>Another lower pres, but more GPM.
>
>It's for future generations to know what you were thinking.
>And LOL when people don't round to nearest 5 GPM, or have ANY significant 
>digits right of the decimal point in pres.
>
>Saw a retail store, 22' high, with 17 PSI reqd at base of riser. How's that 
>work? Zero loss piping?
>
>
>George L.  Church, Jr., CET  
>Rowe Sprinkler Systems, Inc.
>PO Box 407, Middleburg, PA 17842
>877-324-ROWE       570-837-6335 fax
>[email protected]
>
>
>
>-----Original Message-----
>From: [email protected] 
>[mailto:[email protected]] On Behalf Of Greg McGahan
>Sent: Tuesday, July 19, 2011 4:23 PM
>To: [email protected]
>Subject: Hydraulic Data Plates
>
>Is it the intent of the Hyd Data Plate to:
>
>1) Identify the MOST demanding area calculated  OR
>2) to identify the most demanding area of Hazard calculated?
>
>I always thought you only needed one plate for the most demanding area of a 
>single system. but I see some risers that have 2,3 or more hyd plates.
>
>What is / was the intent?
>Greg
>--
>Greg McGahan
>Living Water Fire Protection, LLC <http://www.livingwaterfp.com>
>1160 McKenzie Road
>Cantonment, FL 32533
>850-937-1850
>fax 850-937-1852
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to