A single riser/system may have several different areas and each may have a different demand.
You'll need a separate HDP fire each area you calc to prove the Hydraulics work based upon your pipe size used. Example: Combination MFG with warehouse and office area, total of say 40,000 sq ft. Easy single riser. Ware house of 20,000 sf has rack storage that is the most demanding part of the system. So let's say you need a 6" main feeding 2" branch lines to a 4" main on the opposite side of a grid. You may not feel like doing a separate calc for the 10,000 Sf mfg area, so you just extend the grid over the mfg area which is closer to the riser. No additional data plate required as long as MFG demand is less than storage demand, and design area is equal or less. If the MFG area is farther than the storage area from the riser you'll have to do a proof calc. to show you'll meet the required MFG area demand. If you do one post it. Let's say the last 10,000 Sf is office area. Are you really going to install a 6x4x2 grid in an office? Not unless you know it will someday become MFG or warehouse area. So you do a LH calc for the office. Since your installation is based upon that calc. you need to post it. The only time we don't post calc's we've done, is when the AHJ doesn't believe we have calc'ed the most remote or most demanding area. We do the "Proof Calc." for the AHJ Only! If our calc was right we just put a copy in the file in case it we need it again later. If they were right we use it instead and thank them for catching our miss. -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Greg McGahan Sent: Tuesday, July 19, 2011 2:23 PM To: [email protected] Subject: Hydraulic Data Plates Is it the intent of the Hyd Data Plate to: 1) Identify the MOST demanding area calculated OR 2) to identify the most demanding area of Hazard calculated? I always thought you only needed one plate for the most demanding area of a single system. but I see some risers that have 2,3 or more hyd plates. What is / was the intent? Greg -- Greg McGahan Living Water Fire Protection, LLC <http://www.livingwaterfp.com> 1160 McKenzie Road Cantonment, FL 32533 850-937-1850 fax 850-937-1852 _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)