Thank you Craig. 

Bobby Gillett
Sr. Project Manager
Key Fire Protection, Inc.
(731) 424-0130 office  (731) 424-9285 fax 
(731) 267-4853 cell
www.keyfireprotection.com
 
 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Thursday, September 15, 2011 11:17 AM
To: [email protected]
Subject: RE: Entrance/Exit Canopy?!

I wouldn't consider this a canopy or porte-cochere but rather an extension
of the horizontal exit or exit corridor.   If you look at 8.15.7.4 the only
allowance for omission of sprinklers in such exterior exit corridors is when
the walls are 50% open.  Doesn't sound like this exemption is met by this
installation.

The architect would have to include this tube in his egress length
calculations since you are not technically "out of the building" until you
reach the end of the tube.  

Just at a quick glance it would sound like you may have to extend sprinklers
the length of the tube.

It will be interesting to see how the AHJ interprets this section of 13.



Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SCĀ  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Bobby Gillett
Sent: Thursday, September 15, 2011 10:06 AM
To: [email protected]
Subject: RE: Entrance/Exit Canopy?!

Thank you - you actually walk through this tube to get to the front door of
the office from the parking lot. It is attached to the building and self
supported and sits on the ground. It has a flat walk in it that is about 5'
to 6' wide. It looks like a piece of pipe that is sitting on its side on the
ground and has settled in just enough to create a flat walk, if this makes
any sense. 

Bobby Gillett
Sr. Project Manager
Key Fire Protection, Inc.
(731) 424-0130 office  (731) 424-9285 fax 
(731) 267-4853 cell
www.keyfireprotection.com
 
 
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Gerald
Schulhoff
Sent: Thursday, September 15, 2011 8:39 AM
To: [email protected]
Subject: RE: Entrance/Exit Canopy?!


If the tube is not suspended and open on the sides I do not think it will
qualify as a canopy or porte-cochere.If the floor is flat and hard  storage
could be problem, even if you asked the local AHJ and get approval a change
in reviewer can stop your project. Gerald Schulhoff SET
Firewater Design(804) [email protected]> From:
[email protected]
> To: [email protected]
> Subject: RE: Entrance/Exit Canopy?!
> Date: Wed, 14 Sep 2011 16:29:32 -0500
> 
> I should have mentioned this facility is Production/Manufacturing with an
> office.
> 
> Thank you, Tom.
> 
> Bobby Gillett
> Sr. Project Manager
> Key Fire Protection, Inc.
> (731) 424-0130 office  (731) 424-9285 fax 
> (731) 267-4853 cell
> www.keyfireprotection.com
>  
>  
> 
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Bobby
Gillett
> Sent: Wednesday, September 14, 2011 3:17 PM
> To: [email protected]
> Subject: Entrance/Exit Canopy?!
> 
> I have a project I am bidding on that has an alternate for an entrance
> "tube"; this is a non-combustible steel "tube" 30'-0 long and 16'-0 wide.
> The beams are circular and are spaced horizontal to the building entrance
> door/wall and the skin of the "tube" is perforated aluminum (perforation
> size is unknown). Can I apply NFPA 13 2007 8.15.7.2 to this scenario? 
> 
>  
> 
> Thank you,
> 
>  
> 
> Bobby Gillett
> 
> Sr. Project Manager
> 
> Key Fire Protection, Inc.
> 
> (731) 424-0130 office  (731) 424-9285 fax 
> 
> (731) 267-4853 cell
> 
>  <http://www.keyfireprotection.com> www.keyfireprotection.com
> 
>  
> 
>  
> 
>  
> 
> -------------- next part --------------
> An HTML attachment was scrubbed...
> URL:
>
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
> s/20110914/e344340f/attachment.html>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> -----
> No virus found in this message.
> Checked by AVG - www.avg.com
> Version: 10.0.1392 / Virus Database: 1520/3896 - Release Date: 09/14/11
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
                                          
-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
s/20110915/6e22c0dd/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

-----
No virus found in this message.
Checked by AVG - www.avg.com
Version: 10.0.1410 / Virus Database: 1520/3898 - Release Date: 09/15/11

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

-----