EC's = 5 heads minimum and can't lower the density.

Ron Fletcher
Aero Automatic
Phoenix, AZ





-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Matt Grise
Sent: Thursday, October 20, 2011 11:38 AM
To: '[email protected]'
Subject: RE: Density Area Question

You could specify in your proposal that you have done the OH2 equivalent of 
.2/1500. 

This sounds like maybe an older spec that was update with a new head but the 
density did not get updated? Is the specifying engineer very familiar with fire 
sprinklers?



Matt Grisé PE*, LEED AP 
Sales Engineer 
Alliance Fire Protection 
130 w 9th Ave.
North Kansas City, MO 64116

*Licensed in KS & MO 

913.888.0647 ph 
913.888.0618 f 
913.927.0222 cell 
www. AFPsprink.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Brian Harris
Sent: Thursday, October 20, 2011 12:46 PM
To: [email protected]
Subject: Density Area Question

I'm having a brain cramp and could use some help. I'm working on a retail
store and the engineer has called for Tyco EC-11 heads with a .18/2500
density. I realize the .18/2500 falls on the OH-2 curve but the cut sheet
for the head is rated at .20/1500 for OH-2. How would you go about designing
to these specs?

 

Brian Harris, CET

First Defense Fire Protection

11957 Ramah Church Road

Huntersville, NC 28078

Phone: 704.948.3506

Fax: 704.948.3507

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20111020/76690320/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to