Calc what Code/Listing requires: .20 / 1500,

but produce an "Auxilliary" Calc at the .18/2500.

Use the bigger pipe(s) of the two. You will probably have a BIG safety
margin at the .2/1500

Jeff Garrison
Detroit Automatic Sprinkler


On Thu, Oct 20, 2011 at 1:46 PM, Brian Harris <[email protected]>wrote:

> I'm having a brain cramp and could use some help. I'm working on a retail
> store and the engineer has called for Tyco EC-11 heads with a .18/2500
> density. I realize the .18/2500 falls on the OH-2 curve but the cut sheet
> for the head is rated at .20/1500 for OH-2. How would you go about
> designing
> to these specs?
>
>
>