Bob,

I'd go to my Lubrizol rep for this. The language seems a little too limp to
hang a hat on.

On Thu, Oct 20, 2011 at 3:34 PM, Bob <[email protected]> wrote:

> I'll try to answer my own question in part.  13, 9.3.3.2 states, "shall
> consist of flexible fittings or flexible piping".  Under the Advantages
> heading Blazemaster states " Flexibility in the piping for greater ease of
> installation"  and "Greater resistance to seismic activity than copper or
> steel systems".  Based on this it seems to me that the expansion loop would
> suffice.   Can anyone back this up or demonstrate why it's incorrect?
>
> Thanks,
>
> Bob Knight, CET III
> 208-318-3057
> www.firebyknight.com
>
>
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Bob
> Sent: Thursday, October 20, 2011 1:09 PM
> To: [email protected]
> Subject: Seismic Separation Assembly
>
> In regard to seismic separation assemblies,  are they required for CPVC
> piping?  If they are, does the expansion loop that blazemaster requires
> satisfy the requirement?
>
> Thanks,
>
> Bob Knight, CET III
> 208-318-3057
> www.firebyknight.com
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20111020/f33b07a4/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to