I believe you have a case for classifying what you're doing as a maintenance item, not designing a new system to a new criteria. If you needed to change a 1/2" SR SSP sprinkler in a corridor of a hospital, would you be required to replace with QR, and then replace ALL the heads in the corridor (or smoke compartment) with QR as well? Not the intent....
George L. Church, Jr., CET Rowe Sprinkler Systems, Inc. PO Box 407, Middleburg, PA 17842 877-324-ROWE 570-837-6335 fax [email protected] -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Justin Reid Sent: Tuesday, November 15, 2011 7:44 AM To: [email protected] Subject: Re: NFPA 14 65 to 100 psi Pressure It sounds like there are two issues here. Was the original system automatic? and what will be the residual pressure of the design? If the original pump was providing 65 psi for the standpipe system then the original system was automatic (Class II like Ron suggested? Potentially Class III?) You should verify the classification of the original standpipe system (I,II,III) and find out if it was designed as automatic or manual. Make sure there is no agreement between the building department and the owner that would be driving a different requirement from the original design (or driving the original design). If it is truly a pump replacement and not part of some larger project, where the design may have changed, then you should be able to push for original design...like for like replacement of the pump. It may just take some more explaining to the AHJ about the specifics of the repair work. And like George stated, they should always provide a code citation. Justin Reid On Mon, Nov 14, 2011 at 10:29 PM, 321 <[email protected]> wrote: > In a related matter...anyone had an AHJ require upgrade to 100 psi > from 65 psi when replacing a bad Fire Pump ? I have one I am fighting > now in an existing fully sprinkled building less than 75' in Florida. > The AHJ says it must be upgraded in the change out to provide 100 psi. > The Florida uniform building code says that a Fully Sprinkled building > under 75' need have only a manual-wet standpipe. > > Any thoughts on this? > > John W. Farabee > > > > > > ________________________________ > From: Justin Reid <[email protected]> > To: [email protected] > Sent: Mon, November 14, 2011 3:25:25 PM > Subject: Re: NFPA 14 65 to 100 psi Pressure > > Thanks for the quick response! > > Justin Reid > > On Mon, Nov 14, 2011 at 3:20 PM, Steve Leyton > <[email protected] > >wrote: > > > 1993 > > > > > > Steve Leyton > > > > > > > > > > -----Original Message----- > > From: [email protected] > > [mailto:[email protected]] On Behalf Of > > Justin Reid > > Sent: Monday, November 14, 2011 12:20 PM > > To: [email protected] > > Subject: NFPA 14 65 to 100 psi Pressure > > > > Does anyone recall off the top of their heads which edition of NFPA > > 14 the pressure requirements for 2 1/2 inch hose outlets went from > > 65 psi to > > 100 > > psi? > > > > Thanks, > > > > Justin Reid > > -------------- next part -------------- An HTML attachment was > > scrubbed... > > URL: > > <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/at > > tach ments/20111114/c779adc5/attachment.html> > > _______________________________________________ > > Sprinklerforum mailing list > > [email protected] > > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > _______________________________________________ > > Sprinklerforum mailing list > > [email protected] > > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > > -------------- next part -------------- An HTML attachment was > scrubbed... > URL: > < > http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attac > hments/20111114/00a23dc3/attachment.html > > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > -------------- next part -------------- An HTML attachment was > scrubbed... > URL: < > http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attac > hments/20111114/b345a3d3/attachment.html > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > -------------- next part -------------- An HTML attachment was scrubbed... URL: <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20111115/cff38b9c/attachment.html> _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum