Are you in a rural area were the he may be concerned about his fire truck
providing adequate pressure to work his new hose nozzles that want a 100
PSI. 

Thank you,
Andy

Andy Johnston | Master Craft Plumbing and Fire Protection
 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of 321
Sent: Tuesday, November 15, 2011 8:23 AM
To: [email protected]
Subject: Re: NFPA 14 65 to 100 psi Pressure

Yes...code required Class II & Sprinkler 30 years ago when building was
built. 
Original pump is 500 GPM (locked up...and scrap) limited service 30
Horsepower. 
AHJ first required controller jump to internal auto transformer then came
back 
with this 100 psi deal. Customers electric service and emergency gen set
won't 
handle the load.

AHJ is saying he wants pump and standpipe now to comply with current 100 psi

requirements...so I said ...ok...in that case he only needs a pump if his 
sprinkler demand on the 5th floor requires it. AHJ is now delaying approval
of 
change out while he tries to manufacture a counter to our last submittal
....he 
has had it for 15 days now and seems to be stumped. BTW...5th floor calcs
need 
the 500 gpm at 65 + city to work as piped. Best all around deal is to R & R 
existing pump/controler....owner has 3: identical buildings like this all
built 
at the same time ...so we are trying to get the deal right the first time
with 
the city.

 John W. Farabee





________________________________
From: Ron Greenman <[email protected]>
To: [email protected]
Sent: Mon, November 14, 2011 11:01:05 PM
Subject: Re: NFPA 14 65 to 100 psi Pressure

So why a pump to begin with? Class II pipe?

On Mon, Nov 14, 2011 at 7:29 PM, 321 <[email protected]> wrote:

> In a related matter...anyone had an AHJ require upgrade to 100 psi from 65
> psi
> when replacing a bad Fire Pump ? I have one I am fighting now in an
> existing
> fully sprinkled building less than 75' in Florida. The AHJ says it must be
> upgraded in the change out to provide 100 psi. The Florida uniform
> building code
> says that a Fully Sprinkled building under 75' need have only a manual-wet
> standpipe.
>
> Any thoughts on this?
>
>  John W. Farabee
>
>
>
>
>
> ________________________________
> From: Justin Reid <[email protected]>
> To: [email protected]
> Sent: Mon, November 14, 2011 3:25:25 PM
> Subject: Re: NFPA 14 65 to 100 psi Pressure
>
> Thanks for the quick response!
>
> Justin Reid
>
> On Mon, Nov 14, 2011 at 3:20 PM, Steve Leyton <[email protected]
> >wrote:
>
> > 1993
> >
> >
> > Steve Leyton
> >
> >
> >
> >
> > -----Original Message-----
> > From: [email protected]
> > [mailto:[email protected]] On Behalf Of Justin
> > Reid
> > Sent: Monday, November 14, 2011 12:20 PM
> > To: [email protected]
> > Subject: NFPA 14 65 to 100 psi Pressure
> >
> > Does anyone recall off the top of their heads which edition of NFPA 14
> > the
> > pressure requirements for 2 1/2 inch hose outlets went from 65 psi to
> > 100
> > psi?
> >
> > Thanks,
> >
> > Justin Reid
> > -------------- next part --------------
> > An HTML attachment was scrubbed...
> > URL:
> > <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attach
> > ments/20111114/c779adc5/attachment.html>
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> -------------- next part --------------
> An HTML attachment was scrubbed...
> URL:
> <
>http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
s/20111114/00a23dc3/attachment.html
>l
> >
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> -------------- next part --------------
> An HTML attachment was scrubbed...
> URL: <
>http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
s/20111114/b345a3d3/attachment.html
>l
> >
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
s/20111114/07631e57/attachment.html>

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
s/20111115/f1a6dd2f/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to