NFPA 20 (2010) Section 14.2.5.2.3.1.  "Where simultaneous operation of the 
multiple pumps is possible or required as part of a system design, the 
acceptance test shall include ALL PUMPS operating simultaneously."  What is the 
rationale for "all pumps" versus required pumps to meet design?  Is it purely 
for maintaining the suction header velocity below 15 ft/s as indicated in 
Supplement 4, Technical/Substantive Changes from the 2007 Edition to the 2010 
Edition of NFPA 20?  There is no reference indicating the cumulative flow 
required.  Would system demand flow be used to meet this requirement since the 
pumps are already being flowed at higher necessary flows to conform to Section 
14.2.5.2.4?  Could it be to determine the capabilities of the electrical power 
supply to all pumps is in simultaneous operation?  Additionally, I can find no 
indication of what sizing the test piping or number of connections need to be 
used for such a scenario.

Thoughts?

Ryan L. Hinson, EIT, SET
Senior Fire Protection Engineer, Aviation & Facilities Group
Burns & McDonnell
Minneapolis-St. Paul Office
8201 Norman Center Drive, Suite 300
Bloomington, MN 55437
Direct: 952-656-3662
Fax: 952-229-2923
[email protected]
www.burnsmcd.com<BLOCKED::www.burnsmcd.com>


Proud recipient of PSMJ's Premier Award for Client Satisfaction

-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20111206/a2e100d7/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to