It also supports "not" requiring that the method resulting in the greatest 
demand be used. In LH there are many methods of determining the remote area but 
no requirement that the most demanding method be used.


Ron Fletcher
Aero Automatic
Phoenix, AZ



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Todd Williams
Sent: Wednesday, December 07, 2011 5:15 AM
To: [email protected]
Subject: Re: Multiple design methods in one building

In the Handbook commentary, it states "It is possible for a combination of 
design methods to be used in a single building". I perceive the purpose of this 
section is to make it the designer's discretion on which approach to use, so an 
authority cannot mandate something different after the fact (unless 
specifically included as part of a job specification). I think you are good 
mixing it up. 


At 06:59 AM 12/7/2011, you wrote:
>Reading the following from NFPA 13 2010 ed.  Does this mean the room design 
>method cannot be used in an area if we already used the density/area method in 
>another area? We have a residence with a mechanical penthouse using the 
>density/area method but the floors below are all residential units separated 
>by block walls. Are we be allowed to use room design method for that?
>
>
>11.2.3.1.1 The water supply for sprinklers shall be determined
>*only from one* of the following, at the discretion of the
>designer:
>(1) Density/area curves of Figure 11.2.3.1.1 in accordance
>with the density/area method of 11.2.3.2
>(2) The room that creates the greatest demand in accordance
>with the room design method of 11.2.3.3
>(3) Special design areas in accordance with 11.2.3.4
>-------------- next part --------------
>An HTML attachment was scrubbed...
>URL: 
><http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20111207/55489866/attachment.html>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to