Justin,

Remote still means "far away; distant" in my dictionary. Putting the adverb
on just classifies the "what is remote" aspect. The hydraulically remote
part of the system is probably the water source (as in the case of a
building in San Francisco, the most hydraulically remote part of all
systems is the Hetch Hetchy Watershed in the Sierra Nevada). I picking nits
and using a crazy example but remote is the wrong word, has always been the
wrong except where hydraulically remote and hydraulically most demand just
happen to coincide, and will remain so unless the definitions are changed.
Don't paint stripes on a horse and call it a zebra.

On Wed, Dec 7, 2011 at 11:32 AM, Justin Reid
<[email protected]>wrote:

> You need to put "hydraulically" in front of remote to look at the intent.
> It has been shortened to be called the remote area but the intent is to be
> the hydraulically remote area.
>
> Justin Reid
>
> On Wed, Dec 7, 2011 at 1:47 PM, Fairchild, Jack <
> [email protected]
> > wrote:
>
> > That was last month's discussion, but since I'm feeling particularly
> > punchy...  I'll agree to drop the term "remote area" when NFPA 13 does.
> >  What's really funny is that NFPA 13 uses it both ways!
> >
> > 8.17.2.2
> > (1) Buildings located in remote areas that are inaccessible for fire
> > department support.
> > and
> > 22.3.3
> > (15)* Diagram to accompany gridded system calculations to indicate flow
> > quantities and directions for lines with sprinklers operating in the
> remote
> > area.
> >
> >
> > Jack Fairchild
> >
> > -----Original Message-----
> > From: [email protected] [mailto:
> > [email protected]] On Behalf Of Ron Greenman
> > Sent: Wednesday, December 07, 2011 10:30 AM
> > To: [email protected]
> > Subject: Re: Multiple design methods in one building
> >
> > I really wish we'd just drop the term "remote area" as it only applies
> when
> > the the hydraulically most demanding area is actually also the most
> remote.
> > I know what you mean but lots of folks out there really think the terms
> > are synonymous.
> >
> > On Wed, Dec 7, 2011 at 6:38 AM, Fairchild, Jack <
> > [email protected]
> > > wrote:
> >
> > > I believe you are saying:  Calculate the most remote area using the
> > > appropriate method.
> > > For example:  A 1500 sq.ft. remote area in a corridor will probably be
> > > more demanding that a corridor calculation, but because it is not an
> > > appropriate method you don't do it.
> > >
> > > Jack Fairchild
> > >
> > >
> > > -----Original Message-----
> > > From: [email protected] [mailto:
> > > [email protected]] On Behalf Of
> > > [email protected]
> > > Sent: Wednesday, December 07, 2011 9:26 AM
> > > To: [email protected]
> > > Subject: RE: Multiple design methods in one building
> > >
> > > I am referring to the methods of determining a light hazard remote
> area.
> > > Room design, area density and corridor are the ones I remember. Each
> > method
> > > is allowed and each will result in a different flow requirement. There
> is
> > > no requirement to design the sprinkler system to the most demanding.
> > >
> > >
> > > Ron Fletcher
> > > Aero Automatic
> > > Phoenix, AZ
> > >
> > >
> > >
> > >
> > > -----Original Message-----
> > > From: [email protected] [mailto:
> > > [email protected]] On Behalf Of Fairchild, Jack
> > > Sent: Wednesday, December 07, 2011 6:59 AM
> > > To: [email protected]
> > > Subject: RE: Multiple design methods in one building
> > >
> > > Ron,
> > >
> > > Please clarify your statement.  Which "methods" are your referring to?
> > >  Are you talking about Hazen-Williams vs. Darcy-Weisbach?
> > >
> > >
> > > Jack Fairchild
> > >
> > > -----Original Message-----
> > > From: [email protected] [mailto:
> > > [email protected]] On Behalf Of
> > > [email protected]
> > > Sent: Wednesday, December 07, 2011 8:45 AM
> > > To: [email protected]
> > > Subject: RE: Multiple design methods in one building
> > >
> > > It also supports "not" requiring that the method resulting in the
> > greatest
> > > demand be used. In LH there are many methods of determining the remote
> > area
> > > but no requirement that the most demanding method be used.
> > >
> > >
> > > Ron Fletcher
> > > Aero Automatic
> > > Phoenix, AZ
> > >
> > >
> > >
> > > -----Original Message-----
> > > From: [email protected] [mailto:
> > > [email protected]] On Behalf Of Todd Williams
> > > Sent: Wednesday, December 07, 2011 5:15 AM
> > > To: [email protected]
> > > Subject: Re: Multiple design methods in one building
> > >
> > > In the Handbook commentary, it states "It is possible for a combination
> > of
> > > design methods to be used in a single building". I perceive the purpose
> > of
> > > this section is to make it the designer's discretion on which approach
> to
> > > use, so an authority cannot mandate something different after the fact
> > > (unless specifically included as part of a job specification). I think
> > you
> > > are good mixing it up.
> > >
> > >
> > > At 06:59 AM 12/7/2011, you wrote:
> > > >Reading the following from NFPA 13 2010 ed.  Does this mean the room
> > > design method cannot be used in an area if we already used the
> > density/area
> > > method in another area? We have a residence with a mechanical penthouse
> > > using the density/area method but the floors below are all residential
> > > units separated by block walls. Are we be allowed to use room design
> > method
> > > for that?
> > > >
> > > >
> > > >11.2.3.1.1 The water supply for sprinklers shall be determined
> > > >*only from one* of the following, at the discretion of the
> > > >designer:
> > > >(1) Density/area curves of Figure 11.2.3.1.1 in accordance
> > > >with the density/area method of 11.2.3.2
> > > >(2) The room that creates the greatest demand in accordance
> > > >with the room design method of 11.2.3.3
> > > >(3) Special design areas in accordance with 11.2.3.4
> > > >-------------- next part --------------
> > > >An HTML attachment was scrubbed...
> > > >URL: <
> > >
> >
> http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20111207/55489866/attachment.html
> > > >
> > > >_______________________________________________
> > > >Sprinklerforum mailing list
> > > >[email protected]
> > > >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> > >
> > > Todd G. Williams, PE
> > > Fire Protection Design/Consulting
> > > Stonington, CT
> > > 860.535.2080
> > > www.fpdc.com
> > >
> > > _______________________________________________
> > > Sprinklerforum mailing list
> > > [email protected]
> > > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> > >
> > >
> > > _______________________________________________
> > > Sprinklerforum mailing list
> > > [email protected]
> > > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> > >
> > > _______________________________________________
> > > Sprinklerforum mailing list
> > > [email protected]
> > > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> > >
> > >
> > > _______________________________________________
> > > Sprinklerforum mailing list
> > > [email protected]
> > > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> > >
> > > _______________________________________________
> > > Sprinklerforum mailing list
> > > [email protected]
> > > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> > >
> >
> >
> >
> > --
> > Ron Greenman
> > Instructor
> > Fire Protection Engineering Technology
> > Bates Technical College
> > 1101 So. Yakima Ave.
> > Tacoma, WA 98405
> >
> > [email protected]
> >
> > http://www.bates.ctc.edu/fireprotection/
> >
> > 253.680.7346
> > 253.576.9700 (cell)
> >
> > Member:
> > ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC
> >
> > They are happy men whose natures sort with their vocations. -Francis
> Bacon,
> > essayist, philosopher, and statesman (1561-1626)
> > -------------- next part --------------
> > An HTML attachment was scrubbed...
> > URL: <
> >
> http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20111207/ea5fee97/attachment.html
> > >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> -------------- next part --------------
> An HTML attachment was scrubbed...
> URL: <
> http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20111207/77503b98/attachment.html
> >
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20111207/9944e3bc/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to