Does your state allow an ordinance to require more than the state code?

Is it possible to appeal to your state building department.

I would place the call to the state level. I have had a local ordinance
overturned in Ohio by an over zealous local city. 


Arthur Tiroly
ATCO Fire Protection Design
Tiroly and Associates
24400 Highland Rd rm 25, CLE 44143
216-621-8899
216-570-7030 Cell
WWW.ATCOfirepro.com

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Dewayne
Martinez
Sent: Friday, December 16, 2011 2:00 PM
To: [email protected]
Subject: RE: IBC - building separations

Yes, it is written in their local ordinance that all sprinkler systems shall
comply with NFPA 13.

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Cahill,
Christopher
Sent: Friday, December 16, 2011 11:59 AM
To: [email protected]
Subject: RE: IBC - building separations

Is there a legal written ordinance prohibiting 13R? 

Chris Cahill, PE*
Senior Fire Protection Engineer
Aviation & Facilities Group
Burns & McDonnell
P:  952.656.3652
F:  952.229.2923
[email protected]
www.burnsmcd.com
*Lic. in MN


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Dewayne
Martinez
Sent: Friday, December 16, 2011 11:55 AM
To: [email protected]
Subject: RE: IBC - building separations

The owner is having a hard time trying to understand why 5 miles down the
road he can sprinkle his complex with 13R but in this town he needs full 13.
He is pro-sprinkler and has even sprinkled the townhomes in the other
complexes we have done with him.  Unfortunately, putting in dry systems will
price these units out of the market for the area and he, of course, doesn't
want to lose money so the whole project may be canceled.  I have tried for a
variance before with this AHJ.
At the town meeting, when the board asked him why he does not recognize 13R,
his response was that "he feared for the safety of his men".  What, the
other fire departments In the area don't care? 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of George Church
Sent: Friday, December 16, 2011 11:41 AM
To: [email protected]
Subject: RE: IBC - building separations

I certainly know not all AHJs put roadblocks in the way, I was referring
solely to this one that doesn't allow 13R or 13D where appropriate.

We do a lot of small 13R's and I disagree with the recent change to full
-blown water supplies for 13R. Imagine a 10-room motel, 20 sprinklers at
@250 = $5,000 Then your difference is:
Water supply is 30 minutes x 20 GPM or 600 gallons and a 20 GPM unlisted
pump $3,000 complete OR under 13 Water supply is 30 minutes x 40 GPM or 1200
gallons, and an NFPA 20 fire pump for 50 GPM, NFPA 20 wiring,
controller....$25,000 or more.
Can't think a pressure tank per 22 would be much cheaper than $25,000
installed; 1800 GPM capacity, air compressor, monitoring.

If an AHJ wants to require 13 only, I think they should be forced to
sprinkle their own domiciles. Might change their minds.

George L.  Church, Jr., CET
Rowe Sprinkler Systems, Inc.
PO Box 407, Middleburg, PA 17842
877-324-ROWE       570-837-6335 fax
[email protected]



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Letterman,
Todd
Sent: Friday, December 16, 2011 12:32 PM
To: [email protected]
Subject: Re: IBC - building separations

Not all AHJs and some were in the same field you were before deciding
another path for a multitude of reasons. 

----- Original Message -----
From: George Church [mailto:[email protected]]
Sent: Friday, December 16, 2011 09:27 AM
To: [email protected] <[email protected]>
Subject: RE: IBC - building separations

Why do AHJs put roadblocks in the way of life safety residential systems?
13 only isn't going to get many voluntary systems installed.
So if you're off the water mains in this jurisdiction and want to sprinkler
your house cause you know the value, can you really afford it if you've got
the water supply options of an NFPA 22 compliant pressure tank or an NFPA 22
compliant tank and NFPA 20 fire pump with 30 minutes stored water????
Maybe that's where the NAHB gets their pricing...clean agent might be a
reasonable alternative given the water supply cost.

If you wanted to sprinkler your house in that jurisdiction, you install the
cpvc above ceilings after rough-in inspection, cover it with drywall without
drops but mark on YOUR plan where the exact location is, get final
inspection and bring the feed main out from hiding, drill thru and gle the
drops in, and smuggle a 13D tank and pump into the building. No permit, no
approvals, no inpsection, and boy I'd sleep far better at night knowing I
had one mortgage for the house and a 13D system protecting my family. They
pretty much economically prohibit the installation in daylight and force you
to do it illegally.

George L.  Church, Jr., CET
Rowe Sprinkler Systems, Inc.
PO Box 407, Middleburg, PA 17842
877-324-ROWE       570-837-6335 fax
[email protected]



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Dewayne
Martinez
Sent: Friday, December 16, 2011 12:16 PM
To: [email protected]
Subject: RE: IBC - building separations

It's a multi-family (4unit) building that the owner is trying to make into
2-2 unit townhomes where they could omit sprinklers. 
This particular AHJ only recognizes NFPA 13 and with all the cathedral
ceilings and pitched roofs the owner  does not want all the drains for the
trapped attic pipe or the cost of a dry system.  We do complexes with this
owner all over the area so we are just trying to help him out of a jamb. 
If the AHJ will not budge the owner is probably going to build the attic and
roof with fire retardant treated wood and the sprinklers will be omitted
from the attic.  

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Jim Davidson
Sent: Friday, December 16, 2011 11:01 AM
To: [email protected]
Subject: RE: IBC - building separations

First you need to find what the building is classified as? Is it a
multi-family dwelling or a one or two family dwelling? Once the
classification is determined then you need to see if the fire separation
between the dwelling units met the requirements of the IBC. In the area
where we practice the 2006 IBC is still in effect and requires a two hour
fire rated wall.    

In IBC 2006 Edition, Chapter 7, Section 704, paragraph 704.11 "Parapets"
Item No. 5 states that  "In Groups R-2 and R-3 where the entire building is
provided with a Class C roof covering, the exterior wall shall be permitted
to terminate at the underside of the roof sheathing or deck in Type III, IV
and V construction, provided: 
        5.1.    The roof sheathing or deck is constructed of approved
noncombustible materials or of fire-retardant-treated   wood for a distance
of 4 feet (1220 mm);" 
Paragraph 705.6 "Vertical Continuity" Item no. 4 states: "      In buildings
of Type III, IV and V construction, walls shall be permitted to terminate at
the underside of combustible roof sheathing or decks provided:
        4.1.    There are no openings in the roof within 4 feet (1220 mm) of
the fire wall, 
        4.2.    The roof is covered with a minimum Class B roof covering,
and
        4.3.    The roof sheathing or deck is constructed of
fire-retardant-treated wood for a distance of 4 feet (1220 mm)  on both
sides of the wall or the roof is protected with 5/8 inch (15.9 mm) Type X
gypsum board directly beneath   the underside of the roof sheathing or deck,
supported by a minimum of 2-inch (51 mm) nominal ledgers attached to    the
sides of the roof framing members for a minimum distance of 4 feet (1220 mm)
on both sides of the fire wall."

The 2009 IBC has similar wording but in a different section of Chapter 7
because of renumbering. 

Regards

Jim Davidson 
 
Davidson Associates
Fire Protection * Medical Gas * Code Consulting 302-994-9500  
Fax:302-234-1781


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Dewayne
Martinez
Sent: Friday, December 16, 2011 8:31 AM
To: SprinklerFORUM
Subject: IBC - building separations

Where is the spot in the IBC that defines what rating a wall must be to
divide a larger building into two smaller, separate ones?

I remember talk about row housing in San Francisco where one large building
was subdivided into separate townhomes by use of firewalls.

Thanks,

 

Dewayne Martinez

Design Build Fire Protection

-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
s/20111216/9efeba2c/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to