Wouldn't requesting and being granting a "variance" from the town during
an board meeting prevent this? They have power to amend and adopt the
laws for their community so I don't see why they don't have power to
provide a variance.  We still meet state sprinkler code for this
building. 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Cahill,
Christopher
Sent: Friday, December 16, 2011 5:04 PM
To: [email protected]
Subject: RE: IBC - building separations

Not really good news at all. It was established the law says 13 in that
community, doesn't matter if it's right or wrong, it's the law.  The AHJ
can't just waive the law.  If anything ever happens Dewayne will be on
the hook for not following the law.  Well and the GC too, but he's not
the sprinkler expert.  It's win-lose for Dewayne.  He will have no
defense.

You do this on the forum often enough:
Prosecution: 'Mr. Martinez, may I call you Screwed, the correspondence
in front of you shows you knew the local law specified NFPA 13.  Why did
you argue for and ultimately install 13R contrary to    the law?'
Mr. Martinez: 'No you may not, I'm not Screwed (yet).  Because the law
was dumb, the GC went to the politicians and the City Administrator made
a decision to keep business in town and the Fire        Marshal
approved.'
Prosecution: 'And do any of those people you mention including yourself
have the power over the will of the People of this fine community that
wanted full 13?  Isn't that a form of Communism or a     Dictatorship?
You are aware what a Republic is, right?  You know the representatives
of the People upheld the law on appeal before any of this happened?'
Mr. Martinez: 'I wouldn't know I'm a sprinkler contractor.'
Prosecution: 'So once again business, corrupt politicians and ignoring
law won over these dead people?'
Mr. Martinez: 'Well, maybe I am Screwed.'

Of course that's hyperbole.  Not saying I wouldn't do the 13R either,
but I'd sure try to pass liability.  The win-win comes if you get an
ordinance change before the City council ASAP to go back to the base 13R
where allowed by the model codes.

Chris Cahill, PE*
Senior Fire Protection Engineer
Aviation & Facilities Group
Burns & McDonnell
P:  952.656.3652
F:  952.229.2923
[email protected]
www.burnsmcd.com
*Lic. in MN



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of George
Church
Sent: Friday, December 16, 2011 4:25 PM
To: [email protected]
Subject: RE: IBC - building separations

Hallelujah!!!

Win-win indeed. Keep that variance handy, you could get a lot of mileage
out of it. It was ok for them, so its ok for us in this next one, right?
Topped off a good week with a winner- time to go decorate the Flamingo
Lounge for Christmas.

Thanks for the great news.

George L.  Church, Jr., CET
Rowe Sprinkler Systems, Inc.
PO Box 407, Middleburg, PA 17842
877-324-ROWE       570-837-6335 fax
[email protected]



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Dewayne
Martinez
Sent: Friday, December 16, 2011 4:18 PM
To: [email protected]
Subject: RE: IBC - building separations

The state does allow local municipalities to adopt a more stringent fire
code.  This gets confusing for both contractors and builders.
On a better note, politics have played a positive role in my situation.
After the builder met with the city administrator voicing their concerns
about having to pull out of building the complex if they were forced to
go full 13, the fire department has decide it is now ok to go with 13R.
I think they realized it was better to bend and go with 13R rather than
lose all the tax revenue, site and utility improvements that the builder
was going to provide.  Win-win for all parties involved!

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Art
Tiroly
Sent: Friday, December 16, 2011 1:26 PM
To: [email protected]
Subject: RE: IBC - building separations

Does your state allow an ordinance to require more than the state code?

Is it possible to appeal to your state building department.

I would place the call to the state level. I have had a local ordinance
overturned in Ohio by an over zealous local city.


Arthur Tiroly
ATCO Fire Protection Design
Tiroly and Associates
24400 Highland Rd rm 25, CLE 44143
216-621-8899
216-570-7030 Cell
WWW.ATCOfirepro.com

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Dewayne
Martinez
Sent: Friday, December 16, 2011 2:00 PM
To: [email protected]
Subject: RE: IBC - building separations

Yes, it is written in their local ordinance that all sprinkler systems
shall comply with NFPA 13.

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Cahill,
Christopher
Sent: Friday, December 16, 2011 11:59 AM
To: [email protected]
Subject: RE: IBC - building separations

Is there a legal written ordinance prohibiting 13R?

Chris Cahill, PE*
Senior Fire Protection Engineer
Aviation & Facilities Group
Burns & McDonnell
P:  952.656.3652
F:  952.229.2923
[email protected]
www.burnsmcd.com
*Lic. in MN


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Dewayne
Martinez
Sent: Friday, December 16, 2011 11:55 AM
To: [email protected]
Subject: RE: IBC - building separations

The owner is having a hard time trying to understand why 5 miles down
the road he can sprinkle his complex with 13R but in this town he needs
full 13.
He is pro-sprinkler and has even sprinkled the townhomes in the other
complexes we have done with him.  Unfortunately, putting in dry systems
will price these units out of the market for the area and he, of course,
doesn't want to lose money so the whole project may be canceled.  I have
tried for a variance before with this AHJ.
At the town meeting, when the board asked him why he does not recognize
13R, his response was that "he feared for the safety of his men".  What,
the other fire departments In the area don't care?

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of George
Church
Sent: Friday, December 16, 2011 11:41 AM
To: [email protected]
Subject: RE: IBC - building separations

I certainly know not all AHJs put roadblocks in the way, I was referring
solely to this one that doesn't allow 13R or 13D where appropriate.

We do a lot of small 13R's and I disagree with the recent change to full
-blown water supplies for 13R. Imagine a 10-room motel, 20 sprinklers at
@250 = $5,000 Then your difference is:
Water supply is 30 minutes x 20 GPM or 600 gallons and a 20 GPM unlisted
pump $3,000 complete OR under 13 Water supply is 30 minutes x 40 GPM or
1200 gallons, and an NFPA 20 fire pump for 50 GPM, NFPA 20 wiring,
controller....$25,000 or more.
Can't think a pressure tank per 22 would be much cheaper than $25,000
installed; 1800 GPM capacity, air compressor, monitoring.

If an AHJ wants to require 13 only, I think they should be forced to
sprinkle their own domiciles. Might change their minds.

George L.  Church, Jr., CET
Rowe Sprinkler Systems, Inc.
PO Box 407, Middleburg, PA 17842
877-324-ROWE       570-837-6335 fax
[email protected]



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
Letterman, Todd
Sent: Friday, December 16, 2011 12:32 PM
To: [email protected]
Subject: Re: IBC - building separations

Not all AHJs and some were in the same field you were before deciding
another path for a multitude of reasons.

----- Original Message -----
From: George Church [mailto:[email protected]]
Sent: Friday, December 16, 2011 09:27 AM
To: [email protected] <[email protected]>
Subject: RE: IBC - building separations

Why do AHJs put roadblocks in the way of life safety residential
systems?
13 only isn't going to get many voluntary systems installed.
So if you're off the water mains in this jurisdiction and want to
sprinkler your house cause you know the value, can you really afford it
if you've got the water supply options of an NFPA 22 compliant pressure
tank or an NFPA 22 compliant tank and NFPA 20 fire pump with 30 minutes
stored water????
Maybe that's where the NAHB gets their pricing...clean agent might be a
reasonable alternative given the water supply cost.

If you wanted to sprinkler your house in that jurisdiction, you install
the cpvc above ceilings after rough-in inspection, cover it with drywall
without drops but mark on YOUR plan where the exact location is, get
final inspection and bring the feed main out from hiding, drill thru and
gle the drops in, and smuggle a 13D tank and pump into the building. No
permit, no approvals, no inpsection, and boy I'd sleep far better at
night knowing I had one mortgage for the house and a 13D system
protecting my family. They pretty much economically prohibit the
installation in daylight and force you to do it illegally.

George L.  Church, Jr., CET
Rowe Sprinkler Systems, Inc.
PO Box 407, Middleburg, PA 17842
877-324-ROWE       570-837-6335 fax
[email protected]



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Dewayne
Martinez
Sent: Friday, December 16, 2011 12:16 PM
To: [email protected]
Subject: RE: IBC - building separations

It's a multi-family (4unit) building that the owner is trying to make
into
2-2 unit townhomes where they could omit sprinklers.
This particular AHJ only recognizes NFPA 13 and with all the cathedral
ceilings and pitched roofs the owner  does not want all the drains for
the trapped attic pipe or the cost of a dry system.  We do complexes
with this owner all over the area so we are just trying to help him out
of a jamb.
If the AHJ will not budge the owner is probably going to build the attic
and roof with fire retardant treated wood and the sprinklers will be
omitted from the attic.

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Jim
Davidson
Sent: Friday, December 16, 2011 11:01 AM
To: [email protected]
Subject: RE: IBC - building separations

First you need to find what the building is classified as? Is it a
multi-family dwelling or a one or two family dwelling? Once the
classification is determined then you need to see if the fire separation
between the dwelling units met the requirements of the IBC. In the area
where we practice the 2006 IBC is still in effect and requires a two
hour fire rated wall.

In IBC 2006 Edition, Chapter 7, Section 704, paragraph 704.11 "Parapets"
Item No. 5 states that  "In Groups R-2 and R-3 where the entire building
is provided with a Class C roof covering, the exterior wall shall be
permitted to terminate at the underside of the roof sheathing or deck in
Type III, IV and V construction, provided:
        5.1.    The roof sheathing or deck is constructed of approved
noncombustible materials or of fire-retardant-treated   wood for a
distance
of 4 feet (1220 mm);"
Paragraph 705.6 "Vertical Continuity" Item no. 4 states: "      In
buildings
of Type III, IV and V construction, walls shall be permitted to
terminate at the underside of combustible roof sheathing or decks
provided:
        4.1.    There are no openings in the roof within 4 feet (1220
mm) of
the fire wall,
        4.2.    The roof is covered with a minimum Class B roof
covering,
and
        4.3.    The roof sheathing or deck is constructed of
fire-retardant-treated wood for a distance of 4 feet (1220 mm)  on both
sides of the wall or the roof is protected with 5/8 inch (15.9 mm) Type
X
gypsum board directly beneath   the underside of the roof sheathing or
deck,
supported by a minimum of 2-inch (51 mm) nominal ledgers attached to
the
sides of the roof framing members for a minimum distance of 4 feet (1220
mm) on both sides of the fire wall."

The 2009 IBC has similar wording but in a different section of Chapter 7
because of renumbering.

Regards

Jim Davidson

Davidson Associates
Fire Protection * Medical Gas * Code Consulting 302-994-9500
Fax:302-234-1781


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Dewayne
Martinez
Sent: Friday, December 16, 2011 8:31 AM
To: SprinklerFORUM
Subject: IBC - building separations

Where is the spot in the IBC that defines what rating a wall must be to
divide a larger building into two smaller, separate ones?

I remember talk about row housing in San Francisco where one large
building was subdivided into separate townhomes by use of firewalls.

Thanks,



Dewayne Martinez

Design Build Fire Protection

-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attach
ment
s/20111216/9efeba2c/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to