Builders and developers do take note of these things occasionally. There is
a developer in the DC area that requires base building sprinkler systems in
their buildings to be designed as ordinary hazard occupancies. This is not
done because of the actual occupancy, but to get enough sprinklers (and
safety factor) to accommodate tenant revisions. They were burned in the past
with the low builder using maximum spacing and minimum safety factor to
achieve the smallest pipe sizes. Unfortunately, the first tenant into this
multi-story office building required so many additional sprinklers, that the
Fire Marshal required calculations. They didn't even come close to working.
It took a lot of work to get calcs to work (by running additional pipe to
create loops) and to keep from having to tear a brand new system out and
start over.


Mike Hill

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Steve Leyton
Sent: Friday, January 06, 2012 1:13 PM
To: [email protected]
Subject: RE: Frozen pipe, a rant

Doug:

Matt's comment is tongue-in-cheek, but spot on.   The problem is that a
life-safety system that often requires thoughtful and conceptual design
basis is generally brought to market by a process that rewards a bidder for
leaving stuff out.  At least occasionally.  If the code or referenced
standards doesn't prescribe it, and the project documents don't require it,
then you're exponentially lessening your chances of obtaining the work if
you include it in a competitive proposal.  The bottom line answer to your
question (or rant, as the case may be) is that a more proactive approach
isn't undertaken organically because there is little or no demand for
excellence or a standard of care above and beyond the minimum prescribed by
code.  Until building developers and owners perceive value in what we do,
and demand a higher standard of care than "Adequate", then the situation you
describe will not only continue to occur, it will prevail.

Steve Leyton




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Douglas Hicks
Sent: Friday, January 06, 2012 10:06 AM
To: [email protected]
Subject: Frozen pipe, a rant

As I bill out yet another frozen pipe repair, I am wondering why there is
not any input from the sprinkler trade concerning insulation methods to
prevent frozen pipes.  

We had a motel that had a problem with frozen pipes. The owner had the
blown-in insulation removed. The pipes were repaired and the pipes tented
with plastic and then insulation blown in. No problems for 5 years. 

We have a facility that had the attic piping protected by tenting plastic
over the pipes, then insulation blown in.  After 20 + years, we have had no
problems with frozen pipes. 

Another facility has insulation batts under the pitched roof.  The pipes are
in the warm attic and after 10 years, we have had no problems with frozen
pipes.

I have no idea what the insulation costs are in new construtcion,  but I am
sure not as much in repairing busted pipes,  not to mention ruined ceilings,
damaged goods and stocks.  

Then there are those building with the large ventilation louvers in the
gable ends.  The wind blows in and moves the insulation, exposing the
piping.

I am done, I will save my comments about Schedule 5 and 10 for another time.


-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attach
ments/20120106/5a050cff/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to