And holds 150+ PSI when its flowed, if a manual wet with <100 PSI on it from 
city.....
If there are PRV FHVs, it would be nice to know they're set for 40 PSI instead 
of 110 PSI, as at Meridian in Phila.
Would have saved the Phila FD several hours it took to get a sprinklerfitter on 
site with the special Giacomini wrench.
Imagine if they'd been able to get wet stuff on the fire hours sooner?
Hey, maybe there IS value to these tests!


George L.  Church, Jr., CET  
Rowe Sprinkler Systems, Inc.
PO Box 407, Middleburg, PA 17842
877-324-ROWE       570-837-6335 fax
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Morey, Mike
Sent: Wednesday, January 11, 2012 8:54 AM
To: [email protected]
Subject: RE: standpipe pressure beginnings

If I had to venture a guess, testing a manual standpipe verifies that it is 
free of obstruction as well as damage/leaks/etc?
 
Mike Morey, SET, CFPS
Sprinkler Designer
BMW Constructors, Inc.
O: 317.651.0596 | C: 317.586.8111
www.bmwc.com

________________________________

From: [email protected] on behalf of Todd Williams
Sent: Wed 1/11/2012 8:45 AM
To: [email protected]
Subject: RE: standpipe pressure beginnings



There are some buildings here that go back to the 1930s. The hospital was 
started in 1912, but I don't think anything is that old. Finding old building 
codes could be challenging. Standpipes may have even been retrofits. Unless 
there is date stamped on an original device, there may be no way of telling. 
Their records of construction are not that complete. I will probably have to 
make assumptions on age and come to some agreement with the AHJ. I think the 
best we are going to get is something that meets the intent of 25 based on what 
we can find.

BTW, What is the purpose of testing a manual standpipe? I can understand with 
an automatic system because you are checking for water supply decline. As long 
as their haven't been any design changes and there are no pressure reducing 
devices, I can't see what problems could arise. The water supply boosted 
through a truck is going to more of a function of the apparatus than any 
internal building system. I don't get it.


At 08:19 PM 1/10/2012, you wrote:
>I've come across that before.  With and without building pumps.  I 
>asked and was told 'you tell us'.
>With an external piece I'd limit the FDC pressure to 175 and try for 
>500, 250, 250..  For lack of no other suggestion.  Close the FCV's.
>I've had 3" standpipes with 1 3/4" FDV's, 2 1/2" with 1 1/2".  You 
>really need to find what BC was in place, read it, and then find what 
>edition of 14 was referenced, if any.  Gauge the hydrant, gauge the 
>FDC, don't trust the piece's (or Bldg. FP's) gauges for everything.
>Welcome aboard. 
>TD
>
>
>When were standpipes first stipulated to have a minimum pressure? I 
>would assume that at some point there was no minimum pressure standard 
>(in the days prior to hydraulic calculations). I am dealing with 
>buildings up to 100 years old.
>
>Todd G. Williams, PE
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


-------------- next part --------------
A non-text attachment was scrubbed...
Name: winmail.dat
Type: application/ms-tnef
Size: 5582 bytes
Desc: not available
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120111/7f88a2ea/attachment.bin>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to