Manufacturer's data sheets!!!

Steve 




-----Original Message-----
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Seidl Jamie D.
Sent: Thursday, April 05, 2012 9:01 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: k -- WHAT?

I was looking at that too... and scratching my head. K=50 for 100 psi @ 500 
seems to always work out in the field.

-----Original Message-----
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Steve Leyton
Sent: Thursday, April 05, 2012 11:57 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: k -- WHAT?

Um, Ron?  According to that chart a 2.5" angle valve will flow 9.9gpm at 
100psi.   I don't think that's quite in accordance with HW.

If you are flowing 250 through the valve at 100psi, it has a K of 25.0, no?   
But they can flow more ...  K at 350gpm/100psi would be 35 ...   What are you 
trying to do?

Steve 



-----Original Message-----
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Ron Greenman
Sent: Thursday, April 05, 2012 8:49 AM
To: sprinklerforum@firesprinkler.org
Subject: Re: k -- WHAT?

http://www.westerndynamics.com/Download/friclossfittings.pdf

On Thu, Apr 5, 2012 at 8:46 AM, Seidl Jamie D. <jdse...@vscfs.com> wrote:

> Are you looking for friction loss through a valve, or are you looking 
> to flow a certain amount of water at a certain pressure?
>
> -----Original Message-----
> From: sprinklerforum-boun...@firesprinkler.org [mailto:
> sprinklerforum-boun...@firesprinkler.org] On Behalf Of Vince Sabolik
> Sent: Thursday, April 05, 2012 11:45 AM
> To: sprinklerforum@firesprinkler.org
> Subject: k -- WHAT?
>
> Good morning --
>
> Anyone have an approximate K value for a 2½" hose valve?
>
>
>
>
> Vince Sabolik, West Tech Fire Protection, Inc.
> 11351 Pearl Road / Strongsville, Ohio
> 44136       440 238-4800     Fax 440 238-4876
> ____________________________________________________________________
>
>
> -------------- next part -------------- An HTML attachment was 
> scrubbed...
> URL: <
> http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attac
> hments/20120405/bddfbfe1/attachment.html
> >
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@firesprinkler.org
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@firesprinkler.org
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>



--
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

rgreen...@bates.ctc.edu

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon, 
essayist, philosopher, and statesman (1561-1626)
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120405/48e6124f/attachment.html>
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to