I am curious to know how many of you have had an AHJ require a full blown flow 
test be submitted with 13D calculations? 13D only requires a static pressure 
reading from the job site address. Reason being, it is understood that a 13D 
system demand (two heads flowing, 26gpm) will not over-run a municipal water 
system. The flow test is only required for buildings that fall under the NFPA 
13 standard. The cost of a flow test can be very expensive and time consuming. 
Contractors must wait for the water purveyor to conduct the test.


If an AHJ requires a flow test for a 13D system, and since 13D does not require 
a flow test, doesn't the AHJ have to get approval from the State Fire Marshal 
and/or Building Standards Commission to require this expensive (and 
unnecessary) test?


It seems to me that the only reason a plan checker would require a flow test 
for a 13D system is because they don't understand or recognize the reason 
behind a flow test. 


Any suggestions on how to educate a plan checker without making them look bad 
would be appreciated.


Regards,
Owen Evans