Someone needs to explain to me why I need a flow test on anything that
merely flows 30 or so gpm unless my pressure demand is near my city static.

On Wed, Apr 11, 2012 at 9:57 AM, IPA <[email protected]> wrote:

> By default you need to calc according to 13 (which requires a full flow
> test). The only exception is if you use the simplified calculation method
> described by 13D which is essentially calculating to only a static pressure
> and also requires you to figure in losses through tees on the run and is
> only good for straight run systems (ie. tree), and mains larger than 4" (if
> I recall correctly).
>
>
>
> On Wed, Apr 11, 2012 at 9:29 AM, Gary Stites <[email protected]> wrote:
>
> > If I remember right, if a 13D system is looped or gridded then,
> > technically, it is to be calculated against a curve rather than static
> > pressure, thus requiring a flow test.
> >
> > On Wed, Apr 11, 2012 at 9:20 AM, Owen Evans <[email protected]> wrote:
> >
> > > I am curious to know how many of you have had an AHJ require a full
> blown
> > > flow test be submitted with 13D calculations? 13D only requires a
> static
> > > pressure reading from the job site address. Reason being, it is
> > understood
> > > that a 13D system demand (two heads flowing, 26gpm) will not over-run a
> > > municipal water system. The flow test is only required for buildings
> that
> > > fall under the NFPA 13 standard. The cost of a flow test can be very
> > > expensive and time consuming. Contractors must wait for the water
> > purveyor
> > > to conduct the test.
> > >
> > >
> > > If an AHJ requires a flow test for a 13D system, and since 13D does not
> > > require a flow test, doesn't the AHJ have to get approval from the
> State
> > > Fire Marshal and/or Building Standards Commission to require this
> > expensive
> > > (and unnecessary) test?
> > >
> > >
> > > It seems to me that the only reason a plan checker would require a flow
> > > test for a 13D system is because they don't understand or recognize the
> > > reason behind a flow test.
> > >
> > >
> > > Any suggestions on how to educate a plan checker without making them
> look
> > > bad would be appreciated.
> > >
> > >
> > > Regards,
> > > Owen Evans
> > > -------------- next part --------------
> > > An HTML attachment was scrubbed...
> > > URL: <
> > >
> >
> http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120411/9d3529a9/attachment.html
> > > >
> > > _______________________________________________
> > > Sprinklerforum mailing list
> > > [email protected]
> > > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> > >
> >
> >
> >
> > --
> > Gary Stites
> > 661-213-9379
> >
> > RLH <http://www.rlhfp.com>
> > gstites.tumblr.com
> > Mr. Ricky <http://www.facebook.com/pages/Mr-Ricky/119445524768916>
> > Moondogs Golf Country Club <http://www.moondogscc.com>
> > NBC Worship Team <https://sites.google.com/site/nbcjudah/>
> > facebook.com/gsprink <http://www.facebook.com/gsprink>
> > Pandora Station <http://www.pandora.com/?sc=sh43464983213902734>
> > Hit Record <http://www.youtube.com/watch?v=beQh8jtIarM>
> > -------------- next part --------------
> > An HTML attachment was scrubbed...
> > URL: <
> >
> http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120411/aad97cd2/attachment.html
> > >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> -------------- next part --------------
> An HTML attachment was scrubbed...
> URL: <
> http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120411/53c3aa16/attachment.html
> >
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120411/e603c7e4/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to